Discuss AFDD - Has this left a loophole for landlords? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
Recently been working on a system design for a LL. I was told the building would be a three floor 16 room HMO, so the design was done to the current Regs for that use. When the LL saw the cost of AFDD's he 'blew a fuse' and said no way was he fitting them at a cost of over 3K. I explaned that this was now a legal requirement and that they had to be fitted in HMO's from the new regs come into force. Needless to say he wasn't best pleased.

He come back to me a few days later and said it was not going to be an HMO now but a Hostel instead so he wouldn't be required to fit AFDD's - which is correct from what I can see in the regs.

The thing is that I'm the only one being told that - everything else is still being done (as cheeply as possible from what I can see with the not so occisional stretching of rules and requirements) to facilitate an HMO. Speaking to other trades on-site has borne this out with some telling me they had been told to say it's a hostle if anyone asks, but the building conversion is going ahead as per original instructions for an HMO.

So, have the IET left a risky unintentional loophole here? - Tell the sparks it's a hostel and save yourself some money! It's difficult to call this one out as in some cases there isn't much of a difference between the apperance of a hostel and a HMO but the electrical requirements are very different.

Are we potentially going to end up with a case where a spark doing a EICR or an install certifies to the spec for a Hostel, the LL then runs it as an HMO and if something goes wrong the spark is the fall guy as the LL will say the spark did not tell him the requirements were differrent?? If the LL says it's something it's not how can a certifying make that call and certify to the specs he believes the building is actually being used for?
I can see this becoming an issue with unscrupulous LL's once they twig the loophole - and they are the very ones whos properties are likely to have the problems and the ones that were - I suspect, a big part of the reason why HMO's are now required to fit AFDD's.

Interested to hear peoples views especially anyone on here with IET connections.
 
Have you checked the planning application?
Yes - and the answer........ nothing, zip, zilch, nada, no change of use application at all! Still listed as retail
 
Not surprising. Problem is you know his intentions.

I'd be inclined to adopt a take it or leave it attitude.
Not sure where I'll go with this one, if it goes ahead I'll be making sure HOSTEL in bold is all over the certs!

It's the longer term implications that concern me if this apparent loophole is exploited by lots of HMO LL's.
 
Not sure where I'll go with this one, if it goes ahead I'll be making sure HOSTEL in bold is all over the certs!

It's the longer term implications that concern me if this apparent loophole is exploited by lots of HMO LL's.

Pretty much a certainty that if one landlord has spotted a loophole, it'll soon be in widespread use around BT7 & BT9.
 
Pretty much a certainty that if one landlord has spotted a loophole, it'll soon be in widespread use around BT7 & BT9.
I live in close proximity to BT7 and have had several calls over the past few years from friends of friends who happen to be landlords looking favours done. I've got to the stage now where I tell them I don't touch domestic work, the state of some of the installations is beyond belief. Sadly its only a matter of time before something happens and only then will things (maybe) change
 
I live in close proximity to BT7 and have had several calls over the past few years from friends of friends who happen to be landlords looking favours done. I've got to the stage now where I tell them I don't touch domestic work, the state of some of the installations is beyond belief. Sadly its only a matter of time before something happens and only then will things (maybe) change
Sadly, I fear you may well be correct! I wouldn't touch anything in the Holylands myself either and the more dodgy stuff I see being done by LL's the more I'm inclined to stop doing any LL work at all - apart from a a very few exceptions where it's a 'if it needs it, it gets it' approach and only the best of stuff will do, but there are not too many of those type of LL's about.
 
Sadly, I fear you may well be correct! I wouldn't touch anything in the Holylands myself either and the more dodgy stuff I see being done by LL's the more I'm inclined to stop doing any LL work at all - apart from a a very few exceptions where it's a 'if it needs it, it gets it' approach and only the best of stuff will do, but there are not too many of those type of LL's about.
I'd tend to agree with you, unless you find a (rare) decent one they just want a quick, cheap fix with no regard for safety or regulation. I find it easier to steer clear.
 
Agree on comments the other thing that seems to be appearing is the actual faulty AFDD’S & actually knowing the fault especially on the combined RCBO/ AFDD.
I personally not fitted any yet & hopefully don’t have to
 
Surely, it is the owner's responsibility to ensure that the building complies with legislation, not the electrician's.
As long a you have a written statement in your contract as to the purpose and use of the building, you should be covered legally.
Having said that, if any client of mine tried this kind of tactic, be would no longer be my client.
 
Agree on comments the other thing that seems to be appearing is the actual faulty AFDD’S & actually knowing the fault especially on the combined RCBO/ AFDD.
I personally not fitted any yet & hopefully don’t have to
Yip, they're going to be a pain. Any I've seen so far have some method of indicating the reason for tripping though, but if it's a AFDD activation it's just as likely to be an appliance fault as an install fault.
 
Surely, it is the owner's responsibility to ensure that the building complies with legislation, not the electrician's.
As long a you have a written statement in your contract as to the purpose and use of the building, you should be covered legally.
Having said that, if any client of mine tried this kind of tactic, be would no longer be my client.
The thing is if something happens it comes down to a case of LL's word against the sparks word.

... LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......

Surely this needs sorted out IET??
 
LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......
before the contract .
saying you have declined to have them installed .
you go by the regs not him .
 
The thing is if something happens it comes down to a case of LL's word against the sparks word.

... LL tells spark it's a hostel - (no AFDD required), Spark issues EICR / EIC and off he goes.
.... LL produces 'Satisfactory' cert and gets HMO licence - (with no AFDD's fitted)
.... Something nasty happens and all goes bad. Investigation uncovers a cert for install that hasn't got AFDD's in a building used as an HMO
.... LL, to save his neck, says the spark said it was satisfactory and I took his word for it, he never told me I needed AFDD's and how else was I to know, that's why I got a spark to check out the wiring for me. I'm a responsible LL your Honour, I depended on the Spark to do his job right.
.... Spark says I was told it was a Hostel and did the inspection to the relevant standards in light of what I was told. How would I know a Hostel from an HMO?
.... LL - I said no such thing, just asked for a cert and got it, seems I got a cowboy spark!

It all gets into a nasty one word against the other and at best spark ends up with a very brused reputation by association and at worst.......

Surely this needs sorted out IET??
Which is why I suggested you get in writing (and could also add a note on the EIC) confirming the type and usage of the building. Loophole closed.
 
HMO or Hostel; both would require local authority licensing, in which case I would speak with them FIRST and get it in writing where you would stand as the installer as you believe that LL has unscrupulous intentions.

If that licensing people say no AFFDs required then you are covered (as licensing conditions would be above 7671 [115.1])
 
Okay, just playing a bit of a devils advocate here but what if....

Spark sets out to do an HMO install for a regular LL, no formal contracts, has done lots of work for LL before, all done to the regs with AFDD's. Halfway through the job LL goes - 'what are those things at xx hundred / xx thousand pounds? I've never needed those before'. Spark explains now a legal requirement in an HMO. LL goes away fuming. LL turns up later and says 'I'm not paying for those take them out, it's a hostel not an HMO, don't need them'.

So, what's the chances of getting that in writing? - about zero.
What now ?
Walk away knowing you'll not get a penny for what you've done.
Put up and shut up.
Fit them anyway but only charge for RCBO's and take the hit.
Report to local authority - to which he'll deny all knowledge of the conversation.
I can't see any good option for a spark in this situation.

It just seems odd to me how an HMO has to have AFDD's and a Hostel doesn't when in the practical sense there is very little difference between them apart from the length of a guest / resident's stay. Surely the risk to life and property is similar in both and it would have been easy cover both in the regs.

As for some local authority inspectors picking up on it in the certs, any that I've seen wouldn't know an AFDD from a ciggy packet, all they look for is a big satisfactory or signature on the cert and they're content that someone else is carrying the can if it all goes south.

Like I said, just playing devils advocate here, thankfully I can walk away from this one with no loss, but sooner or later some poor sod is going to get caught out with this. I'm sure that any of us that do work for LL's know at least one or two who are as dodgey as heck.
 
HMO or Hostel; both would require local authority licensing, in which case I would speak with them FIRST and get it in writing where you would stand as the installer as you believe that LL has unscrupulous intentions.

If that licensing people say no AFFDs required then you are covered (as licensing conditions would be above 7671 [115.1])
In this case it's BS7671:2018 421.1.7 would take precedence over local authority requirements as it is a statutory requirement. I stand corrected on that point, still I'd rather work to a recognised standard than what someone in the local authority tells me.

421.1.7
Arc fault detection devices conforming to EN62606 shall be provided for
single phase AC final circuits supplying socket outlets with rated current
not exceeding 32A in:
• Higher risk residential buildings
• Houses of multiple occupancy (HMO)
• Purpose built student accommodation
• Care homes
NOTE 1: Higher Risk Residential Buildings are assumed to be residential
buildings over 18m in height or in excess of six storeys, whichever is met
fi rst. It is anticipated that in many areas, higher risk residential buildings
will be defined in legislation which can be subject to change over time,
as well as in risk management procedures adopted by fi re and rescue
services. Current legislation should be applied.
For all other premises, the use of AFDDs conforming to BS EN62606 is
recommended for single phase AC fi nal circuits supplying socket outlets
not exceeding 32A.

Where used, AFDDs shall be placed at the origin of the circuit to be protected
 
Last edited:
In this case it's BS7671:2018 421.1.7 would take precedence over local authority requirements as it is a statutory requirement.

421.1.7
Arc fault detection devices conforming to EN62606 shall be provided for
single phase AC final circuits supplying socket outlets with rated current
not exceeding 32A in:
• Higher risk residential buildings
• Houses of multiple occupancy (HMO)
• Purpose built student accommodation
• Care homes
NOTE 1: Higher Risk Residential Buildings are assumed to be residential
buildings over 18m in height or in excess of six storeys, whichever is met
fi rst. It is anticipated that in many areas, higher risk residential buildings
will be defined in legislation which can be subject to change over time,
as well as in risk management procedures adopted by fi re and rescue
services. Current legislation should be applied.
For all other premises, the use of AFDDs conforming to BS EN62606 is
recommended for single phase AC fi nal circuits supplying socket outlets
not exceeding 32A.

Where used, AFDDs shall be placed at the origin of the circuit to be protected

Wiring regs aren't statutory, but I'd certainly aim to work within their confines and consider a hostel to fall within the category of 'high risk residential building'.
 
Wiring regs aren't statutory, but I'd certainly aim to work within their confines and consider a hostel to fall within the category of 'high risk residential building'.
I Humbly stand corrected your honour, lol
 
In this case it's BS7671:2018 421.1.7 would take precedence over local authority requirements as it is a statutory requirement. I stand corrected on that point, still I'd rather work to a recognised standard than what someone in the local authority tells me.

421.1.7
Arc fault detection devices conforming to EN62606 shall be provided for
single phase AC final circuits supplying socket outlets with rated current
not exceeding 32A in:
• Higher risk residential buildings
• Houses of multiple occupancy (HMO)
• Purpose built student accommodation
• Care homes
NOTE 1: Higher Risk Residential Buildings are assumed to be residential
buildings over 18m in height or in excess of six storeys, whichever is met
fi rst. It is anticipated that in many areas, higher risk residential buildings
will be defined in legislation which can be subject to change over time,
as well as in risk management procedures adopted by fi re and rescue
services. Current legislation should be applied.
For all other premises, the use of AFDDs conforming to BS EN62606 is
recommended for single phase AC fi nal circuits supplying socket outlets
not exceeding 32A.

Where used, AFDDs shall be placed at the origin of the circuit to be protected
I get your point Jimbo, reason I say that licensing authority is that they'll be backing up their requirements with legislation (housing & local government legislation) as opposed to non-stat BS7671. They'll ultimately be the ones to grant or revoke any license but you would be helping your case with something from them in writing, even if that just means he gets some other schmuck to install what he wants and how it wants it; thier head on that block then, not yours. Reg 29 "...all due diligence to avoid commission of an offence..". It could even be that the licensing authority say it's nowt to do with them and doesn't need licensing; at least then you've explored the avenue and satisfied yourself with how YOU would stand if faeces were flung by fan. Paranoid, overkill? Whatever it needs to be to protect my backside 🤣
 
I get your point Jimbo, reason I say that licensing authority is that they'll be backing up their requirements with legislation (housing & local government legislation) as opposed to non-stat BS7671. They'll ultimately be the ones to grant or revoke any license but you would be helping your case with something from them in writing, even if that just means he gets some other schmuck to install what he wants and how it wants it; thier head on that block then, not yours. Reg 29 "...all due diligence to avoid commission of an offence..". It could even be that the licensing authority say it's nowt to do with them and doesn't need licensing; at least then you've explored the avenue and satisfied yourself with how YOU would stand if faeces were flung by fan. Paranoid, overkill? Whatever it needs to be to protect my backside 🤣
Fair point.
and as for rear end protection - it seems that it is becoming an increasingly major part of the job these days, especially when working with some LL's.

... First law of landlording - carry on being as dodgey as you can get away with unless a force takes action on you.

... Second law of landlording - When a force acts on you accelerate out of the picture and make sure someone else ends up carrying the can.

... Third law of landlording - to every rule there is a equal and opposite dodgy work around!
 
Fair point.
and as for rear end protection - it seems that it is becoming an increasingly major part of the job these days, especially when working with some LL's.

... First law of landlording - carry on being as dodgey as you can get away with unless a force takes action on you.

... Second law of landlording - When a force acts on you accelerate out of the picture and make sure someone else ends up carrying the can.

... Third law of landlording - to every rule there is a equal and opposite dodgy work around!
I totally agree. At the first signs of the landlord being "dodgy", I would immediately stop doing any more work for that landlord.
 
Surely if he registers the property afterwards as a HMO then he would need an EICR done on the property and it would be noted there are no AFDD's
True - but only if he tells the spark it's an HMO.

If the LL decides to save the expense of putting in AFDD's by telling the spark doing the EICR it's a hostel, then it's 'satisfactory' without AFDD's whereas it wouldn't be as an HMO. In alot of cases there's not much physical difference between an HMO and a Hostel so the spark gets dupped into issuing a cert for an install which isn't really up to 7671:2018 spec and no Local authority inspector that I know of would either know to the difference or go past the first page of the cert. So this gets me wondering if the smelly stuff hits the fan and something bad happens, is it likely to become a war of he said / she said played out in a courtroom somewhere?

All a bit hypothetical, but to me it seems that hostel should really be in there with HMO with the AFDD requirements.
 
I think the difference between a hostel and a HMO is a hostel is ‘guests’, whereby appliances are provided and PAT tested, whereas a HMO is residents where any old junk maybe plugged in…

In that instance I can see the difference for the requirements. In this instance I’d run a mile, if they are pulling tricks this early
 
We’re having a similar discussion on another thread concerning dodgy landlords, and I’ll repeat what I’ve said there.

Not all landlords are dodgy.

We only hear about bad ones because it makes headlines/ good telly.

There must be thousands of decent HMO landlords doing things right, and producing low rent housing for disadvantaged tenants.

Yes, there’s a loophole, there always is until it’s discovered and fixed.

Likewise, normal rental properties need an EICR. Have done for years. Only now is short term holiday lets requiring same.
 
We’re having a similar discussion on another thread concerning dodgy landlords, and I’ll repeat what I’ve said there.

Not all landlords are dodgy.

We only hear about bad ones because it makes headlines/ good telly.

There must be thousands of decent HMO landlords doing things right, and producing low rent housing for disadvantaged tenants.

Yes, there’s a loophole, there always is until it’s discovered and fixed.

Likewise, normal rental properties need an EICR. Have done for years. Only now is short term holiday lets requiring same.
100% Correct and I'm one of them - Landlord that is. I have a very simple rule that I go by - If I wouldn't be prepared to move in and live there myself, then it's not good enough to rent out - simples

EICR's in Norn Iron are a bit different in the private rental market - but it is set to change.
 
Surely, it is the owner's responsibility to ensure that the building complies with legislation, not the electrician's.
As long a you have a written statement in your contract as to the purpose and use of the building, you should be covered legally.
Having said that, if any client of mine tried this kind of tactic, be would no longer be my client.
Council attitude where I live if the electrician gives it an EICR he is responsible,many are giving up on HMO's one costly regulation 'upgrade' after another every five years.I used to have unsolicited offers a couple of times a month from those wishing to buy my HMO; nothing in the last few months. Many years ago I was told my council would like to see all HMO closed and every resident in minimaly studio flats, not everyone can afford that particularly now.
 

Reply to AFDD - Has this left a loophole for landlords? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I can't find any really up to date threads on whether we have to fit AFDD's. I am specifically talking about in a domestic premise. I can see...
Replies
42
Views
5K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
43
Views
1K
My mate has family in Southern Ireland and he has been over there a couple of times this year helping them renovate a property. He has been...
Replies
14
Views
1K
We are new landlords and have just got an EICR done. The building is only 5 years old so I am shocked that remedial work has been noted as...
Replies
45
Views
11K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock