Currently reading:
Electricity supply - Maximum Capacity of Connection 18 kVA

Discuss Electricity supply - Maximum Capacity of Connection 18 kVA in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello everyone!

I have a question regarding the electricity supply and the maximum demand.

One energy utility supplies an 18 kVA maximum capacity of electricity for a three-phase connection, and I'm wondering what this means in terms of the appliances and equipment I can safely use without overloading the system.

Could someone please clarify what the maximum capacity of an 18 kVA connection means to normal residentials?

I'm particularly interested in understanding how many appliances I can run simultaneously and what the power limitations are. Any insights or advice would be greatly appreciated.

Is it safe to sign this agreement with an 18 kVA supply?
What is the kVA capacity for a basic electricity connection in Australia?

Thank you in advance!
 
Hello everyone!

I have a question regarding the electricity supply and the maximum demand.

One energy utility supplies an 18 kVA maximum capacity of electricity for a three-phase connection, and I'm wondering what this means in terms of the appliances and equipment I can safely use without overloading the system.

Could someone please clarify what the maximum capacity of an 18 kVA connection means to normal residentials?

I'm particularly interested in understanding how many appliances I can run simultaneously and what the power limitations are. Any insights or advice would be greatly appreciated.

Is it safe to sign this agreement with an 18 kVA supply?
What is the kVA capacity for a basic electricity connection in Australia?

Thank you in advance!

Are you sure about those figures?

If it's a three phase supply as stated, then that's around 26A per phase

If it's a single phase supply, which is more normal, that would be circ 80A

If it is three phase, is it 18kVA per phase (so 80A each phase)

Do you have a photo of your connection/meter - or is this enquiry pre-connection?

"Normal" as I understand is 230V single phase 80A (18kVA)
 
Are you sure about those figures?

If it's a three phase supply as stated, then that's around 26A per phase

If it's a single phase supply, which is more normal, that would be circ 80A

If it is three phase, is it 18kVA per phase (so 80A each phase)

Do you have a photo of your connection/meter - or is this enquiry pre-connection?

"Normal" as I understand is 230V single phase 80A (18kVA)
18KVA would be the total for three phases not per phase as I see it Julie.
 
Which makes it only circ 26A per phase, which appears somewhat low, hence why I think the figures aren't correct.
yup understand what your saying, just never heard the figure mentioned per phase before, as you say, figures probably wrong
 
18KVA would be the total for three phases not per phase as I see it Julie.
Hi Julie, yes, I am 100% sure it's three phases, so why total power is less than 18 kVA (see the attachment)?

My requested maximum demand is about 80A per phase for three phases of electricity connection. My drawing power is about 80A per phase.

Is it safe to get a total 17.21 kVA power supply?
I attached the screenshot. Many thanks.
 

Attachments

  • Screenshot 2023-05-30 at 1.58.11 am.png
    120.8 KB · Views: 16
Hi Julie, yes, I am 100% sure it's three phases, so why total power is less than 18 kVA (see the attachment)?

My requested maximum demand is about 80A per phase for three phases of electricity connection. My drawing power is about 80A per phase.

Is it safe to get a total 17.21 kVA power supply?
I attached the screenshot. Many thanks.
Do you have an existing supply?

If so could you post a photo?

17.21 kVA is 25A per phase on a three phase supply if the 17.21 kVA is the total 3 phase power.

17.21 kVA per phase would be circ 75A per phase.

I suspect the figures are wrong, are they quoting for a single phase supply, or have they just mixed up the figures between single and three phase?

You would need to confirm with them.


Do you have the whole of the specification (with supplier and site/customer details removed) - the extract doesn't contain any real information.
 
Last edited:
Yes, 17.21 kVA is the total 3 phase power.

“ 17.21 kVA per phase would be circ 75A per phase.”
How did you calculate this? If per phase, then using line to neutral voltage which is 230V right?

There is an offer document binding with this agreement but I am asking for it.

What is basic connection power supply in Australia? Is it 100A per phase?
 
In the U.K. it is possible to have for instance a 100A 3 phase supply that would give in the region of 70kva.
however you may agree to have a lower maximum demand that will lower your bill.
so it would be possible to have a max demand of 40kva on a 70kva supply.
peak demand is measured by the meter and if you go over your maximum demand, it costs you a lot more than it would if you had agreed to it originally.
 
Yes, 17.21 kVA is the total 3 phase power.

“ 17.21 kVA per phase would be circ 75A per phase.”
How did you calculate this? If per phase, then using line to neutral voltage which is 230V right?

There is an offer document binding with this agreement but I am asking for it.

What is basic connection power supply in Australia? Is it 100A per phase?

The standard connection is up to 100A single phase or up to 100A per phase on three-phase.

However in rural locations this could be limited to 32A (or 32A per phase) and in non-rural locations is normally limited by a fuse to 80A as a maximum (could be 45A, 60A, 63A.....)

To calculate Amps from kVA

Single phase

I = VA / Volts - so convert kVA to VA (x 1000) then divide by the voltage (normally 230V)

So 17.21 kVA single phase

17.21kVA x1000 = 17210VA

17210VA / 230V = 74.83A

Three-phase

Two ways

1)
Divide the total three phase capacity by 3 then continue as per single phase as above

17.21kVA / 3 = 5.737kVA per phase

5.737kVA x 1000 = 5737VA

5737VA / 230V = 24.9A per phase

2)
Convert kVA to VA

Use the following calculation

I = VA / ( L-L Voltage x sqrt(3))

L-L Voltage is normally 400V (actually 230V x sqrt(3) = 398V)

17210 / ( 400 x sqrt(3)) = 24.9A per phase

The square root of 3 is roughly 1.73
 
Last edited:
Interestingly enough, I was just watching an eFixx video of them in Italy and the norm there is 6kVA single phase / 18kVA 3P and it is accepted if you don't manage your demand sensibly then you have to reset the supply breaker following blackout!
 

Reply to Electricity supply - Maximum Capacity of Connection 18 kVA in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock