Search the forum,

Discuss Help with ceiling light fixture. DIY in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Led light fixture went dim. I replaced it with a new fixture and it won’t power on. I have 120v with a multimeter at the wire. When I wire up the light fixture the outlet in the hall goes to ground and hot reversed. I also have voltage at both neutral and hot wire when it’s wired in. Not sure if that’s normal. I tried to install the old fixture and it won’t power on either. What am I missing?
 
You have a high resistance fault somewhere in the neutral wire. This won't have much effect on the meter reading, because the current drawn by the meter is so small and the voltage dropped across the high resistance fault is almost negligible.
When a significant load is fitted, such as your LED fitting, the situation is reversed, with almost no voltage drop across the fitting, and most of it dropped across the high resistance fault.
 
You have a high resistance fault somewhere in the neutral wire. This won't have much effect on the meter reading, because the current drawn by the meter is so small and the voltage dropped across the high resistance fault is almost negligible.
When a significant load is fitted, such as your LED fitting, the situation is reversed, with almost no voltage drop across the fitting, and most of it dropped across the high resistance fault.
What would cause high resistance? Should I pull the wall outlet and inspect? My wife told me she plugged the vacuum into that outlet and the light fixture shut off. Is my issue at that outlet?
 

Reply to Help with ceiling light fixture. DIY in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock