Hello
What is difference between dc and ac capacitor as dc work on 26v and capacitor work 440v

Capacitors work at a wide range of voltages and perform many functions (smoothing, DC blocking, coupling, motor starting, etc). They are all fundamentally based on two electrodes and a gap though.

Have a Google search.
 
Need to narrow down the question a bit.
If we stick to one type as hinted at, aluminium electrolytic, then a few things are easier to answer.
Basically, these are two sheets of aluminium with two sheets of separator, would very tightly into a spiral - like a toilet roll. The separator, which could be paper or plastic, sets the distance between the sheets. In some types, the aluminium film surface is oxidised, and this oxide layer forms the insulator - the thicker it is, the higher the voltage rating. In others, the plastic (or dry paper) is the insulator.
DC or AC is down to how the insulating layers have been formed, and the internal chemistry. I vaguely recall that if the insulator is a formed oxide layer, then reversing the polarity will "unform" this, destroying the insulating layer and effectively causing the cap to go short circuit. If the insulator is the plastic or paper sheet, then it's inherently bipolar as (contrary to what some electricians have told me in the past*) the plastic doesn't care which way the voltage is.

And once you get into it, there's a lot more to understand regarding ripple currents and stuff like that.
If you apply a steady DC to a cap, then once it's charged, no more current will flow (apart from a small amount of leakage). If there is ripple, or it's AC, then periodic currents will flow - creating heating in the internal resistance (see a specification called ESR - effective series resistance). Any specific capacitor will have a power limit - and hence why there is such a choice of capacitors available. For high-ripple applications you would want something with a low ESR. For an intermittent application (such as a motor start capacitor) it could have a lower rating as it will have time to cool down between uses. But for a non-intermittent application, it would need to cope with the power dissipation over a longer period (such as for a motor run application). And for pulse application (handing short high rise rate pulses instead of sine waves) different design considerations come into play - which are beyond my knowledge.

* I jest not, on one occasion an electrician told me that my data cables could only use one section of the trunking (despite it not being big enough and he'd used the much bigger section for a couple of 2.5mm T&Es) as "it the divider wouldn't insulate if they were swapped round".
 
Need to narrow down the question a bit.
If we stick to one type as hinted at, aluminium electrolytic, then a few things are easier to answer.
Basically, these are two sheets of aluminium with two sheets of separator, would very tightly into a spiral - like a toilet roll. The separator, which could be paper or plastic, sets the distance between the sheets. In some types, the aluminium film surface is oxidised, and this oxide layer forms the insulator - the thicker it is, the higher the voltage rating. In others, the plastic (or dry paper) is the insulator.
DC or AC is down to how the insulating layers have been formed, and the internal chemistry. I vaguely recall that if the insulator is a formed oxide layer, then reversing the polarity will "unform" this, destroying the insulating layer and effectively causing the cap to go short circuit. If the insulator is the plastic or paper sheet, then it's inherently bipolar as (contrary to what some electricians have told me in the past*) the plastic doesn't care which way the voltage is.

And once you get into it, there's a lot more to understand regarding ripple currents and stuff like that.
If you apply a steady DC to a cap, then once it's charged, no more current will flow (apart from a small amount of leakage). If there is ripple, or it's AC, then periodic currents will flow - creating heating in the internal resistance (see a specification called ESR - effective series resistance). Any specific capacitor will have a power limit - and hence why there is such a choice of capacitors available. For high-ripple applications you would want something with a low ESR. For an intermittent application (such as a motor start capacitor) it could have a lower rating as it will have time to cool down between uses. But for a non-intermittent application, it would need to cope with the power dissipation over a longer period (such as for a motor run application). And for pulse application (handing short high rise rate pulses instead of sine waves) different design considerations come into play - which are beyond my knowledge.

* I jest not, on one occasion an electrician told me that my data cables could only use one section of the trunking (despite it not being big enough and he'd used the much bigger section for a couple of 2.5mm T&Es) as "it the divider wouldn't insulate if they were swapped round".

I'd read his other posts as well if I were you.
 
Bit of old thread revival ...

Oh dear, from that page :
"Thus, the frequency of the input signal, which is continuously charged (or discharged), determines the capacitance of the capacitor in AC circuits". Err, the capacitance is fixed by the construction of the cap, it's IMPEDANCE (complex relation to resistance) varies with frequency and is 1/(2*pi*f*C).
 

Reply to How to make capacitor in the Solar Thermal Advice Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock