Those involved with ev charger installs will be aware that we should carry out a site / pre works survey to ascertain the current max load with diversity taken into account and strictly speaking should submit the DNO notification beforehand to give them a chance to come back and tell you a yes, no or permit a 16 amp charger but not a 32 amp etc.. also in the event of a looped supply WPD the DNO around here will often send an engineer out to look at the cut out. is also good where the cut out is very old or a fused neutral as they are still out there.
A lot of companies and installers will just fix the charger to the wall, connect it to a circuit and be gone and cashing the cheque, the customer is none the wiser about cutout, max demand or earthing arrangements as the charger works.

WPD are quite good compared to some in that they provide an online map to tell you whether the local grid has capacity on a traffic light system, if its red then they may refuse the charger being installed full stop. Green then its no problem.
I have only heard of them once coming out and making a company (letting agents with a small office and several evs for lettings viewings etc) disconnect 3 x 32 amp chargers. these were notified after install and the local area was already close to max demand, agents were told disconnect them or have supply turned off.

The ENA on behalf of all the DNOs do produce a useful pdf about cut out types and likely ages which I have included in this thread. it might be of use to people.
 

Attachments

  • Identification of Cut out type and age.pdf
    1.5 MB · Views: 22
Most notifications can be done within one calendar month after installation except in certain circumstances.
for a long time i took that view using the standard DNO form, if all the boxes are ticked correctly then you can notify it after install to the DNO. part p still 30 days.
Obviously if its a looped supply or a ow rated fuse, or not known then you ought to seek clarification from the DNO first.
Had a letter from WPD the DNO around here in October or November last year asking me to send them the notification form before install where normally it would be fine to do afterwards if it falls in one of the amber areas or red areas on there online map as they are trying to maximise and manage capacity in central bath which is already a bit over stretched. they are struggling to meet demand.
Its this lack of network capacity which has stopped the council installing lots of on street and public chargers. they dont have capacity.

SSE are much more relaxed along the road in Wiltshire.
 

Reply to Identification of cut outs and ev chargers in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock