I have three outlets (that I can find) that are showing open neutral. I have 80v across hot and neutral, 120v at hot to ground and 28v neutral to ground.
I also have one switch to a light that I think is on this circuit that is not working. If I pull the switch and wire it directly (white to white and black to black) my tester shows open neutral/ground on the same three plugs. When I ran an extension cord to the wires that goes to the light it will come on.
I have replaced all three outlets and still have the same issue. This is an older single wide trailer that I am trying to help a friend out. Anyone have any thoughts or suggestions on what direction to go?
 
I have three outlets (that I can find) that are showing open neutral. I have 80v across hot and neutral, 120v at hot to ground and 28v neutral to ground.
I also have one switch to a light that I think is on this circuit that is not working. If I pull the switch and wire it directly (white to white and black to black) my tester shows open neutral/ground on the same three plugs. When I ran an extension cord to the wires that goes to the light it will come on.
I have replaced all three outlets and still have the same issue. This is an older single wide trailer that I am trying to help a friend out. Anyone have any thoughts or suggestions on what direction to go?
You need to check the circuit feeding these loads. Find the breakers and cut it off and start opening each receptacle on that dead circuit and you will probably find a loose connection somewhere. It could be a bad connection in the panel but is doubtful. Possibly in a light fixture but try the receptacles first
 
You need to check the circuit feeding these loads. Find the breakers and cut it off and start opening each receptacle on that dead circuit and you will probably find a loose connection somewhere. It could be a bad connection in the panel but is doubtful. Possibly in a light fixture but try the receptacles first
I did that already. I also changed all three outlets plus the the switch that is on that circuit. Best that I can figure out is that I have a broken wire or something that is hidden that I do not know about.I also checked for continuity on the wire to the light and they were good, I also changed all the outlets with the light switch disconnected.
 
I did that already. I also changed all three outlets plus the the switch that is on that circuit. Best that I can figure out is that I have a broken wire or something that is hidden that I do not know about.I also checked for continuity on the wire to the light and they were good, I also changed all the outlets with the light switch disconnected.
If you are reading that low of voltage then some where you have a loose or broken neutral.
 
I 100% agree with you just can’t seem to find it. At this point in time I think it is time to open walls and pull new wire.
I wouldn’t go that far. It would help if you had a tone generator which will allow you to follow the wire that you are hooked to (neutral). They are not expensive and you can buy them from Home Depot or Lowes. Do not use this on a circuit that is live.
 
I wouldn’t go that far. It would help if you had a tone generator which will allow you to follow the wire that you are hooked to (neutral). They are not expensive and you can buy them from Home Depot or Lowes. Do not use this on a circuit that is live.
I did think of a tone generator but I could not find one. The only one I found was for CAT cable. Good idea on that side. Will have to look for one. Any one that you like.
 

Reply to Open neutral on residential outlets in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock