Patio heater (hard wire)

Discuss Patio heater (hard wire) in the UK Electrical Forum area at ElectriciansForums.net

hadley1

DIY
Reaction score
2
Hi all,

I am looking to install a 3kw patio heater spurring off an existing socket (on a ring main) as below:

1. Cable to isolator switch (32 Amp TP&N Rotary Switch Insulated Weatherproof - IP65 | Contactum (DX032AC) - https://www.tlc-direct.co.uk/Products/CMDX032.html)
2. Cable from isolator switch to 16A push switch (16 Amp Time Delay Touch Timer - IP66 | Elkay (560A-1) - https://www.tlc-direct.co.uk/Products/EK560Adash1.html)
3. Cable from 16A switch into patio heater.

Cable will be 1.5mm2 SWA.

Is this proposal OK?

Thanks.
 
Hi all,

I am looking to install a 3kw patio heater spurring off an existing socket (on a ring main) as below:

1. Cable to isolator switch (32 Amp TP&N Rotary Switch Insulated Weatherproof - IP65 | Contactum (DX032AC) - https://www.tlc-direct.co.uk/Products/CMDX032.html)
2. Cable from isolator switch to 16A push switch (16 Amp Time Delay Touch Timer - IP66 | Elkay (560A-1) - https://www.tlc-direct.co.uk/Products/EK560Adash1.html)
3. Cable from 16A switch into patio heater.

Cable will be 1.5mm2 SWA.

Is this proposal OK?

Thanks.
No general advice is any load of 2KW or over needs to be on it's own circuit spurring from an RFC is not advisable, 1.5MM2 is hardly large enough for the 3KW heater load
 
only 2 sockets on a 20A? So is this a radial circuit, and not an RFC as you believe?

If its a radial, then I would say its fine to add this load... its protected by 20A... Is there an RCD for this circuit?

I would use 2.5mm SWA, however, as it will be the same size as the supply cable to the sockets.
 
Yes potentially but it would render the project unfeasible hence why I ask the cable size as I imagine the cost of an electrician will be considerably less if they simply do the terminations.
The Spark as you call him.her will need to size the cable and OCPD and test the installation on completion so it's not just termination that's involved Mate, could be a problem getting someone to do this work if they weren't involved in the complete install, just saying, not just a case of lashing in the cable either length of run and installation method need to be accounted for.
 

Reply to Patio heater (hard wire) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock