Discuss Problem with Mitsu inverter PI-controller in the Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Hello everyone. I have a inverter configuration problem I thought someone here might be able to help with. I'm not looking for a specific solution for my inverter in question, but rather if anyone has encountered this problem and has generic parameter advice to give.

I'm using a Mitsubishi FR-D720S-070SC-EC inverter to control a small 1.5 kW blower. Blower moves air through a filter and Mitsu is using PI-controller to increase flow as filter gets dirtier.

I have my PI-controller setpoint on a 0-10V potentiometer and 4...20 mA process value coming from a differential pressure transmitter. Now, the whole setup works fine... unless the pot is at its minimum setpoint value at 0 V. If the potentiometer is at minimum value, simply nothing happens if I block the filter. The controller is alive and conscious as I can view the controller error value on the Mitsu screen, however error refuses to rise above its rest value which would start to increase the flow. If I increase the setpoint any non-zero value, no matter how minimal, then the controller starts working properly.

I've been banging my head on this but I'm pretty much out of parameter changes to try. I've replaced the inverter but that was not the problem. Most annoying part is that according to my notes I used this exact setup in 2017 and back then there were no problems...
 
This is solved. Praise elder gods.

I didn't touch the parameters any more but added a small 120 ohm resistor to potentiometer. The tiny control voltage it gives is enough to wake up the controller when pot is in minimum position.
 

Reply to Problem with Mitsu inverter PI-controller in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, and thanks in advance for any help that can be given. I had a call out to a factory the other day to connect a new motor the maintenance...
Replies
2
Views
849
Evening all Had a problem this week which has puzzled me a bit Installed a machine last week which has 2 sides to it both doing the same operation...
Replies
11
Views
2K
Hi there. I'm building a house and need some help with the LED lighting design. Lots of experience wiring things, some experience using LEDs (did...
Replies
8
Views
2K
M
Hello all, This is my first post so hope I'm in the right place for my question! I sell single-phase frequency invertors that drive variable-speed...
Replies
5
Views
7K
My customer read on many forums about people suffering to solve a problem with the above Land Rover with regards to a fault code known as P1260...
Replies
5
Views
29K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock