Discuss single phase compressor motor in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
3
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be run at 220-240 v / 460-480v 50Hz. (unusual for 50Hz) At 220-240 volts FLc is 16A plus startup inrush. so I should like to run it at the higher voltage as I have 400v available at the 3 phase DB. I can't find anything on the web not even Brook motor website. Any help would be appreciated. Not come across this motor variant before, see pict below!
Thank you Griffey!
 

Attachments

  • duncan's compressor motor.JPG
    190.5 KB · Views: 9
It's designed to be suitable for normal 230V single phase or 460V single, split phase. This supply arrangement is fairly rare in the UK generally, but is very common in the area I live and work. I've fitted loads of these motors over the years.
The motor would run on 400V taken from 2 phases of a 3 phase supply, but will be down on power.
 
It's designed to be suitable for normal 230V single phase or 460V single, split phase. This supply arrangement is fairly rare in the UK generally, but is very common in the area I live and work. I've fitted loads of these motors over the years.
The motor would run on 400V taken from 2 phases of a 3 phase supply, but will be down on power.
Hi, Thank you for the information, I'll stay with the 230v connections as it's not a good idea to run a compressor under voltage. Are you situated in the USA? re the split phase comment!

regards Griffey
 
No he is based in the UK where there are split phase supplies (460v between lines). Whether this motor was produced for UK use or the States where 460-480v is common who knows.
 

Reply to single phase compressor motor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
657
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
562
I have a small mechanics shop in a rural area with no access to 3 phase. I picked up a air compressor cheap and knowing at a min. I will need a...
Replies
3
Views
2K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock