Currently reading:
Why doesn't my Security Light work?

Discuss Why doesn't my Security Light work? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
I have a Security Light on my patio and until recently it worked fine.
It stopped working and I couldn't decide if it was the LED Floodlight or the separate PIR that had stopped working so I replaced both.
I checked them out first, connected them up and they work fine on my workbench, but then I install them outside and they won't work.
I've attached a wiring diagram showing how they are connected.
It all seems straight forward and the wiring is exactly the same as the old set-up so I'm at a loss as to why they don't operate.
Any useful ideas?
 

Attachments

  • Security Light 01.jpg
    39.4 KB · Views: 9
If they work on a bench, from a different supply, then it's neither the LED light or PIR, it's a fault on the supply from within the house.
Have you checked you have both Live and Neutral (and earth) at the PiR position on the property and that the switched Live and the Neutral are continuous to the LED light,?

Have you tested the old light and PIR on the bench?
 
If they work on a bench, from a different supply, then it's neither the LED light or PIR, it's a fault on the supply from within the house.
Have you checked you have both Live and Neutral (and earth) at the PiR position on the property and that the switched Live and the Neutral are continuous to the LED light,?

Have you tested the old light and PIR on the bench?
To answer your two questions:
1. Yes, I've tested the mains supply to the outside world and it appears to be OK - my AVO tells me it is anyway.
I did wonder if it's my connections at the choccy block in the junction box and/or the PIR; i.e. I'd screwed onto insulation instead of cable, so I've undone everything and checked the screws are clamping onto cable and not insulation. I've even tinned the cable ends so they're solid instead of just twisting the cable cores.
2. When I connected up the old system on the workbench the PIR worked OK with the new flood, but the old flood didn't work - even when connected directly to a supply rather than through the PIR so I guess it was the flood at fault, but I happened to have a brand new, still in the box, PIR available, that's why I changed both.
 

Reply to Why doesn't my Security Light work? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock