Discuss Will the mini (or larger) RCBO fir in the this starbreaker board? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
2 questions..

1. Will the mini Starbreaker RCBO's fit in this board?

Below is a picture of the board and also the type of RCBO I want to fit in? Thanks :)

2. The existing 100mA RCD is type AC. The RCBO's will be Type A. I have never quite got my head around how this 'incorrect' selectivity of RCD's means that blinding is possible. Would not the blinding of the Type AC RCD (due to DC earth leakage) be equally possible with or without the Type A RCBO in place?

20240422_143216.jpg
 

Attachments

  • 20240422_143216.jpg
    183.6 KB · Views: 20
1. Will the mini Starbreaker RCBO's fit in this board?
99% sure yes, they are just about 2 cm shorter in height than the original ones.
Would not the blinding of the Type AC RCD (due to DC earth leakage) be equally possible with or without the Type A RCBO in place?
Yes. But by fitting the Type A you are adding something that will protect anything downstream of it if there is DC leakage on that circuit.
Basically that way around is ok for co-ordination. You have to go from "vague" at origin to "more specialised" as you head down the tree.
You can't do it the other way around. e.g. If you had a Type A main switch, you shouldn't use a type AC downstream.

A diagram I pinched from Napit:
1714122024219.png
 
99% sure yes, they are just about 2 cm shorter in height than the original ones.

Yes. But by fitting the Type A you are adding something that will protect anything downstream of it if there is DC leakage on that circuit.
Basically that way around is ok for co-ordination. You have to go from "vague" at origin to "more specialised" as you head down the tree.
You can't do it the other way around. e.g. If you had a Type A main switch, you shouldn't use a type AC downstream.

A diagram I pinched from Napit:
View attachment 116141
I've seen that diagram Tim and never really questioned it, as it is correct. However, after questioning it, I thought 'why'?
I like your choice of words 'vague' and 'specialised' to help explain. However, that still just sounds sensible rather than actually explaining what additional problem will occur (or danger), by fitting a type A downstream from a type AC.

Example
Case 1: You have a a type AC RCD protecting the whole consumer unit. The RCD is at risk of blinding due to DC earth leakage from potential electronics on all circuits.
Case 2: You use one of the spare MCB's in the above CU to feed an EVCP which has a type A RCD fitted in it. The type AC RCD is still at equal risk of blinding by all the original circuits, it is no worse or better.

I'm thinking that there simply isn't any greater danger by fitting a type A downstream from a type AC, it is simple a poor design. It also wouldn't meet the regulations, again this doesn't mean it's dangerous, but it does mean we are not meeting the regulations which I guess is enough of an argument to fit it as in your picture.

Of course I could just change the main switch for a 30mA type A RCD and pretend the other consumer unit is actually part of that one and it is just one big dual RCD board!

They've spent £9000 on lights but don't want to upgrade the CU's :D
 
Last edited:
Agreed. I wasn’t actually intending to suggest there is any issue with what you suggest, it would work and all devices would work to the best of their abilities.
I was basically trying to say that it’s only a problem if the rcds were reversed as the level of protection decreases as you head further from the origin, and it needs to increase.
I think I didn’t put it very well!
 

Reply to Will the mini (or larger) RCBO fir in the this starbreaker board? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
777
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock