Hello everyone.

I bought some property in northern Michigan. It has underground electric with a transformer already on the property. I would like to put in 2 RV panels that are 50A each. The county will let me do all of the work myself with the exception of hooking up the meter to the transformer (obviously). The meter has to go by the road. I plan to bury the line in conduit. I have included a drawing for reference. So, the questions:

Does the main panel need to be by the meter or can I put it further into the property?
What would be the proper wire size to run the distances I have shown?
If the RV sub panels are 50A and include a 50A breaker, does the main panel need a 50A breaker, too, or some other size?
Does the layout on my drawing look proper or is there a better way to go about this?

Thanks in advance,
Pete


PINEDALE RV ELECTRIC PIC.jpeg
 
Hello everyone.

I bought some property in northern Michigan. It has underground electric with a transformer already on the property. I would like to put in 2 RV panels that are 50A each. The county will let me do all of the work myself with the exception of hooking up the meter to the transformer (obviously). The meter has to go by the road. I plan to bury the line in conduit. I have included a drawing for reference. So, the questions:

Does the main panel need to be by the meter or can I put it further into the property?
What would be the proper wire size to run the distances I have shown?
If the RV sub panels are 50A and include a 50A breaker, does the main panel need a 50A breaker, too, or some other size?
Does the layout on my drawing look proper or is there a better way to go about this?

Thanks in advance,
Pete


View attachment 109324
Yes your panel can be away from the meter but you will need a 50 amp double pole breaker to feed each RV. The size wiring that you will need is # 6
 

Reply to Would like some help with questions about wiring for RV setup on property. in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock