Search for tools and product advice,

Discuss Amtech/Trimble - Excessive Earth Loop Impedance on SWA cables in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi All,

I'm new to Amtech/Trimble and I've been asked to review a model.

I'm looking at circuits that are SWA cables using the armour and an internal conductor as the CPC. There are various earth loop impedance errors listed where the Zs at the load end is too high, but what I can tell, Amtech firstly calculates the Zs using the armour only, and if this is too high it sees it as an error, but it then recalculates using the internal CPC in parallel with the armour to reduce the Zs to an acceptable value. There is a note listed referencing the same cable stating this, so I'm I correct in thinking that even though Amtech says this is an error but it actually isn't because of the note explaining the second calculation? Basically, does the note cancel out the error? It seems a bit ambiguous to me......
 
Sounds like it would be sage to get out your resistivity tables and do a manual check to make sure Zs meets BS7671 requirements. There is listing for armour in regs. As to the software aspect, I would look to the designer of it tech support and question that. for due diligence.
 

Reply to Amtech/Trimble - Excessive Earth Loop Impedance on SWA cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
https://gadsolutions.biz/regulations/swa-as-the-cpc Anyone know how reliable the tables on this website are for determining whether the armouring...
Replies
13
Views
3K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock