no the correct motor for the lift.You need a step up Transformer. I think
Do you mean correct motor for the new voltage?no the correct motor for the lift.
Believe it or not it will run at 208vac I do air Conditioners and I’ve never had a problemI'm looking for help on fixing a car lift for a customer. He bought a used lift that calls for 30 amps at 230 volts but his building only has 120/208 voltage. Should he have the motor changed out or should I boost the voltage somehow? And what would I need.
Really? It keep blowing the fuse and it makes a really bad sound when running. Could be from the weight of the car.I was always under the impression that you need to be within +/- 5% if the voltage. You could be right. Thanks for the replyBelieve it or not it will run at 208vac I do air Conditioners and I’ve never had a problem
Upizzle I've never wired a car lift but where are you getting 208vac from? Is the shopReally? It keep blowing the fuse and it makes a really bad sound when running. Could be from the weight of the car.I was always under the impression that you need to be within +/- 5% if the voltage. You could be right. Thanks for the reply
call your local parts house and order a 208/120vac to 240/120 transformer you will need a 10 KVA transformer single phase which is good for 42 ampsI'm looking for help on fixing a car lift for a customer. He bought a used lift that calls for 30 amps at 230 volts but his building only has 120/208 voltage. Should he have the motor changed out or should I boost the voltage somehow? And what would I need.
Is his shop 3 phase or single phaseUpizzle I've never wired a car lift but where are you getting 208vac from? Is the shop
call your local parts house and order a 208/120vac to 240/120 transformer you will need a 10 KVA transformer single phase which is good for 42 amps
3 phase panelUpizzle I've never wired a car lift but where are you getting 208vac from? Is the shop
call your local parts house and order a 208/120vac to 240/120 transformer you will need a 10 KVA transformer single phase which is good for 42 amps
[automerge]1567556888[/automerge]
Is his shop 3 phase or single phase
Since it’s a 3 phase you will need a 15 KVA 3 phase transformer 208/120 to 240/120 y connection3 phase panel
Thank you,Since it’s a 3 phase you will need a 15 KVA 3 phase transformer 208/120 to 240/120 y connection
Lift pulls 25 amps @ 230vThank you,what do you think of this for just the car lift
I’m proud of you and not a bad price and when I done the math on the transformer it is good for 42 amps good luck and your welcomeThank you, View attachment 51884 what do you think of this for just the car lift
[automerge]1567558412[/automerge]
Lift pulls 25 amps @ 230v
Believe it or not it will run at 208vac I do air Conditioners and I’ve never had a problem
Dpg that’s an old thread so what did I do for you to do the thumbBelieve it or not it will run at 208vac I do air Conditioners and I’ve never had a problem
Dpg that’s an old thread so what did I do for you to do the thumb
I agree and I’m not perfect but I have wired split systems HVAC rated for 240vac single phase at Cargill foods with 208vac single phase and the unit is still running 4 years later. I know I make mistakes but I thought that thread was overIt's only a week old, last reply was on the 4th.
I just wasn't convinced that it was good advice to just run it on the incorrect voltage without any further worries or checks.