Discuss Bulbs flutter with dimmer in the DIY Electrical Advice area at ElectriciansForums.net

PapaBear

DIY
Reaction score
0
I have 3 pendant light fixtures with a total of 540 watts of incandescent bulbs connected to a GE electronic dimmer. The bulbs flutter from bright to dim randomly. I have seen this with LEDs before but not incandescent bulbs. What is wrong?
 
I have 3 pendant light fixtures with a total of 540 watts of incandescent bulbs connected to a GE electronic dimmer. The bulbs flutter from bright to dim randomly. I have seen this with LEDs before but not incandescent bulbs. What is wrong?
With incandescent bulbs, this sounds like a loose connection, a failing dimmer, or a dimmer suffering from overload.
What is the rating of your dimmer? It's a bit unusual to have dimmers rated over 500W (I'm in the UK!) though they are available.
 
most dimmers for filament lamps are 400watts max. I've fitted a few 1kW dimmers wherever the load has been > 400w.
 
most dimmers for filament lamps are 400watts max. I've fitted a few 1kW dimmers wherever the load has been > 400w.
I did wonder given this is for 120V, whether dimers in the USA typically had a higher current rating than UK.
A quick google of GE dimmers (in USA) suggests normally rated at 600W for incandescent. One was 750W!
It would be good to know if the OP's is 600W.
 
Thanks for the responses. The switch is rated 600W incandescent at 120v.
One thing I would try would be to take the dimmer out of circuit (eg turn power off and connect the permanent live and switched live together at the switch), turn power back on and see if the flickering continues.
If it does there is something up with the wiring.
Time to call an electrician, or if you are competent with electrics, go round checking all the connections on the circuit, eg tightening screw terminals and checking wire nuts.
 
One thing I would try would be to take the dimmer out of circuit (eg turn power off and connect the permanent live and switched live together at the switch), turn power back on and see if the flickering continues.
If it does there is something up with the wiring.
Time to call an electrician, or if you are competent with electrics, go round checking all the connections on the circuit, eg tightening screw terminals and checking wire nuts.
Good idea. I will give it a try.
 

Reply to Bulbs flutter with dimmer in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I currently have 4 led bulbs in the bathroom and 3 of them arent working. The bulbs that are currently in are LOMAS LED GU10 220-240V 6000k 6w...
Replies
3
Views
521
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
525
I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
945
I fitted a dimmer switch by daisy chaining the dimmer switch to a normal plug. The challenge is the light flickers at random intervals. If I take...
Replies
3
Views
267
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
236

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock