Discuss Class 2 bathroom down light recommendations? in the DIY Electrical Advice area at ElectriciansForums.net

Gibshy

DIY
Reaction score
0
For the bathroom, want them matching and one needs to go over the shower.

Also need to be ok with insulation over the top. Ideally fit in the holes already there and don’t need the plastic huts.

Taken the old ones out and one wire has an earth but the rest don’t, so looking for class 2 (double insulated) fittings.

Can be integral or needing GU10 bulbs.

Just bought some crap ones from Wickes that I won’t be using.
 
Fixed wiring is required to incorporate an earth conductor, whether or not the fitting connected to it requires an earth or not.
If the existing wiring doesn't contain an earth wire, what kind of cable is it? Are the existing fittings 12 volt?
 
Fixed wiring is required to incorporate an earth conductor, whether or not the fitting connected to it requires an earth or not.
If the existing wiring doesn't contain an earth wire, what kind of cable is it? Are the existing fittings 12 volt?

Thanks for your reply.

You are quite right, I’ve taken one down this morning and the cable is twin & earth but the earth has been cut right back.

The back story is that there were originally MR16 fittings and we had a spark come round and change the fittings to GU10s about 8 years ago.

The cable is too short for me to strip back without going into the loft and lifting all the insulation but it looks like that’s what I’m going to have to do.
 

Reply to Class 2 bathroom down light recommendations? in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top