Good morning ,
i am about to set up a pop up shop in a shopping centre. In order to do that i need to provide them with a power draw of the machinary i need.
Tried online but i am not too sure about the result if its correct. So its a crepe machine 3000W at 230 V. Can anybody please help me? Do i have just to divide the W to the V? Many thanks in advance
 
just tell them the watts. (that 3000w = 13A). add anything else you have to give a total.
 
thank you for the answer , they said i cannot go further then 13 amp, so if i plag the crepe machine basically i am done
The crepe machine isn't constantly drawing 13A, it's 'cycling' it on/off to keep the temperature constant. So unless you also need an urn running full-time you'll be fine.
 