Discuss Contactor. Proving dead . 3 phase . in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
2
When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains isolator. Or do I need to 10point check the mains isolator and then another 10point check on the contactor before removing.
Many thanks
 
TL;DR
Contactor. Proving dead. Which points to check. 3 phase
Why does it sound like an exam question to me??

As above, if you’re likely to use a screwdriver on a terminal, use a tester first.

Energising coil may not be 230v, but still test.

Mark everything with tape if not already labelled…. As everything is more than likely all the same colour of cable.
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
 
Whats a 10 point check? how have i survived nearly 50 years in the industry without knowing this
If you have N cables then you have (N * (N-1))/2 pairs to check to know all are safe w.r.t. each other. So for:
  • Single phase (L + N + E) = 3 it is (3*2)/2 = 3 checks
  • 3-phase without N (just L1-3 + E) = 4 it is (4*3)/2 = 6 checks
  • 3-phase normal (L1-3 + N + E) = 5 it is (5*4)/2 = 10 checks
 
Last edited:
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Absolutely, the contactor control could be from a totally separate supply, maybe even UPS-backed!
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Brill thanks. If I was to double check at the contactor. Would you do the 10 checks again or just check the between the phases. Thanks
 
If you have N cables then you have (N * (N-1))/2 pairs to check to know all are safe w.r.t. each other. So for:
  • Single phase (L + N + E) = 3 it is (3*2)/2 = 3 checks
  • 3-phase without N (just L1-3 + E) = 4 it is (4*3)/2 = 6 checks
  • 3-phase normal (L1-3 + N + E) = 5 it is (5*4)/2 = 10 checks
Thanks pc1966, never heard it called that before.
 

Reply to Contactor. Proving dead . 3 phase . in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
499
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
689
i need to purchase a voltage proving unit - i have seen Megger MPU690, Martindale PD690, and Socket and See SP400, and Fluke but difficult to...
Replies
2
Views
440
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock