Hi, I would like to know how I could improve on this board. All opinions
50047
welcome.
 
Agree with above, it would be good to have a service loop of slack in the CPCs, as there is in the L & N. If one of the top circuits in the earth bar needs reterminating after it has been removed for testing or rearrangement of circuits following an alteration, there's hardly any slack available.
 
Heat shrink earth on the box earth. Shorten the earths in the terminals so they are not all poking out on the other side of the terminal. There is one neutral fly lead from the RCBO around the middle that looks like it needs moving up slightly in the terminal. The T&E coming through the back should have been stripped using an electricians knife not ripping out the earth. Cut off the unused bus bar live unless there are more RCBO's to go on. I assume the bus bar (live) cover is going to go on when you are finished? I would try to achieve a straighter line on the neutral fly leads from the RCBO's rather than them all sweeping in as they do. Apart from that lovely!
 
That's seriously tidy work, the only thing I'd think about is whether the CU back openings on a wooden board could compromise the fire enclosure. It's a grey area but if it were in my house I'd want any material completing the enclosure to have a reasonable fire rating.

There's some chat about it on the voltimum site here. In reality it's unlikely ever to be an issue, but worth a thought.
 
Is it just me...or is the bus bar at the bottom awfully close to the base of the consumers unit

It almost looks like it is touching or at best a smoke paper away from touching
 
Why 2 separate feeds?
Is it all on 1 phase?
The main problem you have is the very poor lay out of the panel..
You would have done better yourself building one from scratch..
 
Hello MrShine94
From my perspective and at first glance the terminations other than the Live of the bottom 16A Rcbo ,they look very neat

Is the board spaced out from the Plyboard ? the cables seem to have been squashed between the unit and the Ply
Board is being boxed in and have used some 2 by 1 to bring the board more forward
 
MrShine, regardless of the constructive criticism the quality of your board is in the top 10% and I've seen a lot. No one else advising you has posted pictures of their work as an example for you either. :D You'll find that as you do more you refine certain details but your work is good.
 
Not that im suggesting he has. His board looks stunning and a good job. My experience is that 9 times out of 10 boards i come across that have the earth going through a different entry they also have thw main tails going through different entries to one another.

But in all fairness OP great job looks like you've actually taken pride
 
Not that im suggesting he has. His board looks stunning and a good job. My experience is that 9 times out of 10 boards i come across that have the earth going through a different entry they also have thw main tails going through different entries to one another.

But in all fairness OP great job looks like you've actually taken pride
Earth can go through a different entry to the lines
 
521.5.1 Ferromagnetic enclosures: electromagnetic effects
The conductors of an AC circuit installed in a ferromagnetic enclosure shall be arranged so that all line conductors and the neutral conductor, if any, and the appropriate protective conductor are contained within the same enclosure.
Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferromagnetic material.

Not totally irrelevant @Jon Bateson as some take the above to mean the earth and line conductors should enter at the same point of a DB and there have been a few threads on here regarding this subject where it has been insisted that such must be done in installations by person ordering the work.
 
521.5.1 Ferromagnetic enclosures: electromagnetic effects
The conductors of an AC circuit installed in a ferromagnetic enclosure shall be arranged so that all line conductors and the neutral conductor, if any, and the appropriate protective conductor are contained within the same enclosure.
Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferromagnetic material.

Not totally irrelevant @Jon Bateson as some take the above to mean the earth and line conductors should enter at the same point of a DB and there have been a few threads on here regarding this subject where it has been insisted that such must be done in installations by person ordering the work.
If you are going to quote a reg then at least use the third paragraph
 

Reply to Critical Feedback recent Consumer unit install Please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
803
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock