hi i am replacing a consumer unit over and came across a strange problem with the neutrals when i isolated the old consumer unit. When isolated from supply im still getting 240v between incoming live and out going neutral. I have disconnected all neutrals from block (which clears it from outgoing at main switch) but all circuit neutrals now show still connected to neutral (somewhere). I was thinking it was the obvious old hookey supply, live chopped away but neutral still connected,but it still dosent make sense. Hope someone here can shed a little light on the subject please. Thanks in advance J.A.J
 
i know, weird. i was on it for over an hour before finding a radial the used to feed the immersion heater but was dissed at the load end was the cause.
 
i know, weird. i was on it for over an hour before finding a radial the used to feed the immersion heater but was dissed at the load end was the cause.
Must admit have never experienced this just know the supposed theory behind it so I am just guessing with the test button. Weird stuff this lectricity.
 
i know, weird. i was on it for over an hour before finding a radial the used to feed the immersion heater but was dissed at the load end was the cause.
Ditto same for me, rewire on a TN-S. Found fault N-E on a radial, thought put that to one side while I connect the rest up, except I mixed up the faulty one with another and connected it up. All went well until went to test RCD, which timed out. Test button didn't work either. Took a while before I realised mistake.
 
Is the supply PME by any chance , this situation is something I experienced working for a DNO , where a reverse polarity or broken neutral even externally in an underground joint meant that the neutral became live and returned a live supply via the earth and bonding connections from neighbouring properties .....
 
Last edited by a moderator:
Is the supply PME by any chance , this situation is something I experienced working for a DNO , where a reverse polarity or broken neutral even externally in an underground joint meant that the neutral became live and returned a live supply via the earth and bonding connections from neighbouring properties .....
Hi ,it's a TNS system ,checked the earth coming of cable head (ze 0.30ohms) no return voltage between incoming neutral and earth. It's an old cast 3 fused cable head which also had me thinking about the neighbour scenario but no other cables are coming of it . Had to put the CU back together as had to leave the job cos the customer was going away this morning
 
Is the supply PME by any chance , this situation is something I experienced working for a DNO , where a reverse polarity or broken neutral even externally in an underground joint meant that the neutral became live and returned a live supply via the earth and bonding connections from neighbouring properties .....
No the neutrals not broken coming in as there isn't a voltage on it across earth
 
Is the supply PME by any chance , this situation is something I experienced working for a DNO , where a reverse polarity or broken neutral even externally in an underground joint meant that the neutral became live and returned a live supply via the earth and bonding connections from neighbouring properties .....
No the neutrals not broken coming in as there isn't a voltage on it across earth
Ditto same for me, rewire on a TN-S. Found fault N-E on a radial, thought put that to one side while I connect the rest up, except I mixed up the faulty one with another and connected it up. All went well until went to test RCD, which timed out. Test button didn't work either. Took a while before I realised mistake.
Tested RCD tested within time and test buttons operate as ment to
 
I'm led to believe, if you think of how an RCD works, imbalance between live & neutral, with an earth neutral fault, the fault current in the earth can flow back through the neutral, negating any trip. That's how it was explained to me. But being not expert on the technical bit, however I've had that happen to me.
Yeh I understand that ,but if the neutral conductor for said circuits are connected to neutral bar then shouldn't it still trip
 
And how do you know that , I am simply trying to understand what the op has written , and he's now given more info and not PME , the response I have given is based on an actual situation i have experienced before ....
Hi RG, apologies I seem to have said this the wrong way. What I meant was I believe you and I find it quite scary to that it could happen like that. Cheers, David.
 
If there is a current less than 30mA on more than 1 circuit wouldn't this trip the rcd
Only if the total leakage current reaches 30mA. I did a ramp test on an intermittent trip situation once. The RCD tripped @ 10mA even after we had disconnected all accessories (or so we thought) then we discovered a fused spur feeding an outside light. We disconnected that and tested again, this time it ramped to around 15mA then tripped again. After much searching we found an extension lead plugged in but nothing plugged in that. After unplugging it the rcd ramped up to 30mA no problem. Turns out that the extension lead had a N-E fault.
 
Have you tested between Incoming live and each individual out going disconnected neutral per circuit?
Surely its just a process of elimination until you find the culprit?
 
I'm led to believe, if you think of how an RCD works, imbalance between live & neutral, with an earth neutral fault, the fault current in the earth can flow back through the neutral, negating any trip. That's how it was explained to me. But being not expert on the technical bit, however I've had that happen to me.
Yeh I understand that ,but if the neutral conductor for said circuits are connected to neutral bar then shouldn't it still trip
Have you tested between Incoming live and each individual out going disconnected neutral per circuit?
Surely its just a process of elimination until you find the culprit?
Hi David , I had all circuits disconnected and it cleared it from the neutral bar but all neutral conductors showed a circuit. That's what's doing my head in is that it's not just 1 circuit that seems to be the problem (as yet discovered)
 
Yeh I understand that ,but if the neutral conductor for said circuits are connected to neutral bar then shouldn't it still trip

Hi David , I had all circuits disconnected and it cleared it from the neutral bar but all neutral conductors showed a circuit. That's what's doing my head in is that it's not just 1 circuit that seems to be the problem (as yet discovered)

Right, I'm getting a picture of what you are getting at now, thanks.
So there is either a path to another incoming neutral, or a N-E fault that was not sufficient to trip the original rcd (assuming this was working correctly)?
One other thing that might seem like a daft question, but, have you tried another voltage tester?
 

Reply to Disconnected Neutal Still Showing Connection To Neutral (somewhere) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top