Currently reading:
EICR, no 3A fuse for a fan

Discuss EICR, no 3A fuse for a fan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

My only comment on this thread is that there was a fire in a new build near me, a few years ago, that originated in the bathroom fan. Stalled motor and no 3A fuse in the feed was reported to be the cause.
 
My only comment on this thread is that there was a fire in a new build near me, a few years ago, that originated in the bathroom fan. Stalled motor and no 3A fuse in the feed was reported to be the cause.
My suspicion is that is what the insurer's say to get out of paying.

What do they do in the EU where 3A fuses are practically unheard of?

How is the disconnection level of the fuse, say ~6A = 1.3kW, making a big difference to a fire in such a small area, and are there not thermal cutout to protect the motor, etc.

Yes, I know that the MI says "XYZ" ands we should be following it, but equally it would be interesting to see just what the theoretical modelling of a fault is that allows a 3A fuse to save the day but a 6A MCB is able to cause an inferno.
 
In general I'd rather end up with a shorter list of EICR findings that are actually significant than a long list with some of them being more or less irrelevant.
If I code a missing 3A fuse for a fan it could lead to other findings that are much more important being taken less seriously.
 
Usually the Fan is connected to the lighting supply in a domestic situation & in the bathroom area.
Not seen a switched spur in those situations, which could be awkward to action.
Seems reasonable if required but like I said never seen it done, TBF don’t think I’ve ever coded it or even thought of coding, im looking for the isolation switch only… but may think differently now😎
 
Can’t remember, there used to be a reg that said something like
local isolation for mechanical maintenance should be installed for rotating machinery?
 
Bathroom fans need regular maintenance to remove the build up of skin tissue from them, and there are live exposed terminals (often permanently live) while doing so.
I dont go maintaining/cleaning my fans at night time, so I (radical I know) wander over to the consumer unit and turn off the MCB for the circuit that powers the fan.
 
.................How is the disconnection level of the fuse, say ~6A = 1.3kW, making a big difference to a fire in such a small area, and are there not thermal cutout to protect the motor, etc........................
Most fractional HP motors like bathroom fans are wound in such a way that the winding impedance is high enough to limit the current to safe levels even if the rotor is locked. They're often marked as 'impedance protected' which means the fault current won't rise high enough to cause a temperature rise that's hazardous or likely to cause a fire. This type of motor design usually won't have a thermal fuse on the windings because the normal running temp is pretty close to the locked rotor temp..

Designing a motor to be impedance protected is good practice and very effective but I'd guess that many nameless far East factories would be churning out motors of sloppy design that wouldn't perform this way in real life so I wouldn't have an issue with a local fuse for added protection. Add to this the fact that most are likely to be ClassII with no CPC and therefore no effective RCD protection the hazard becomes increased. I do however wonder where they came up with 3 Amps as an appropriate value for a motor with an RLA/FLA of probably 0.1 - 0.2Amps .... I'd be erring on the side of caution with a 0.5 or 1 Amp fuse if it were my bathroom.
 
Most fractional HP motors like bathroom fans are wound in such a way that the winding impedance is high enough to limit the current to safe levels even if the rotor is locked. They're often marked as 'impedance protected' which means the fault current won't rise high enough to cause a temperature rise that's hazardous or likely to cause a fire. This type of motor design usually won't have a thermal fuse on the windings because the normal running temp is pretty close to the locked rotor temp..

Designing a motor to be impedance protected is good practice and very effective but I'd guess that many nameless far East factories would be churning out motors of sloppy design that wouldn't perform this way in real life so I wouldn't have an issue with a local fuse for added protection. Add to this the fact that most are likely to be ClassII with no CPC and therefore no effective RCD protection the hazard becomes increased. I do however wonder where they came up with 3 Amps as an appropriate value for a motor with an RLA/FLA of probably 0.1 - 0.2Amps .... I'd be erring on the side of caution with a 0.5 or 1 Amp fuse if it were my bathroom.

If the fan is connected to an RCD prorected circuit, then the RCD would still detect an unexpected path back to earth in the event of someone receving a shock, even if the fan itself is class II.
 

Reply to EICR, no 3A fuse for a fan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top