Currently reading:
Electrical Diagrams

Discuss Electrical Diagrams in the Commercial Electrical Advice area at ElectriciansForums.net

V

vaughant

And the importance of being able to read them.

This is a subject that really concerns me with the apprentices where I work and the management staff.
They appear to put no emphasis on what is IMO a fundamental part of electrical control,they seem to prefer getting these lads to either ask someone what the fault is or try guessing first which to me is ludicrous.
I'm not saying I'm perfect (although I have got nice eyes) but I feel I can approach most breakdown situations and given the correct documentation have a damn good chance of saying it's this or that and not just plucking ideas out of the sky that I so often see folk randomly changing components then still looking baffled when it doesn't work.
Of course it's handy to be more lucky than clever but in the real world(or my world at least) luck is a scarce commodity!!!

So,I'm thinking the great folk on here who deal with such instances everyday could maybe contribute some help on this matter with of course pictures and explanations being preferable.

Hopefully this can become some sort of a reference for our good folk who want to get into this relatively untapped field of electrical expertise,after all there's a lot of people out there fitting lights and sockets and as the competition becomes greater in those fields it's my belief that more than a few will look to diversify into the industrial control game.

In my experience our German brothers and sisters do make a damn good diagram but it does require a bit of brain work to see how it all works,again I could be preaching to the converted but I have been amazed by 2 very experienced lads at works inability to even read a basic control diagram,unable to work out where power comes from,not even 100% aware of n/c and n/o switching symbols,fuses,mcb's and forward reverse contactors.

I'll start with this as a basic example.
We had a fault in the week with this motor and I was asked to let the apprentice (3rd year) to lead the way,couldn't get this contactor to kick in.
f4227b61.jpg

Sorry for pic quality.
He stands there with the usual teenage blank expression so I tell him to see what we've got.
He starts rambling and tries a few pointless things like checking nothings tripped etc when I ask him what were looking for.
He has no clue.
We want 78K1 to come in to move the motor towards the wall (shuttle car).
Now,from the diagram under 78K1 is in smaller writing 78.1,apprentice has no idea what this means.
This relates to the page in the diagram where I can find what operates 78K1.
So we go to page 78,section 1,just like a map grid reference .
There we find this.
9f8daf4f.jpg

Jeez I'm sorry for the quality,I'm hoping people with better than an old iPhone camera will chip in!!!
Now,it shows a plc output,an n/c contact from 78K2 before we get to 78K1 A1 then through A2 down to 0v.
People who are familiar with this will know that A1/A2 generally relate to the connections of a contactor coil but those new to this can see it's represented by the symbol of a rectangular box,this often has a diagonal line through it.
In british drawn diagrams it's often shown as a circle but the A1/A2 should give it away.

When control voltage is applied to this coil,it should if working correctly energise and in turn pull the contacts in on the contactor allowing three phase out of the bottom of the contactor and off through various wires to the motor windings.

I then got the apprentice to make the next move.
Again after head scratching it meant me talking him through it.
I got him to check for power at the coil,A1 to 0v rail,nothing showing.
I then got him to check from PLC output A88.0 (A or Q are often used as output symbols, I and E as inputs),we had 24v dc.
The next stage was to check what we had at 78K2 terminals 21/22.
This is where experience comes in,often parts are changed with non original manufacturers ones instead which do not always use the same markings.
This was not the case here but if that occurrs again,the diagram can help as it shows us that were looking for an n/c contact on 78K2.
We tested there and found power to terminal 21,but nothing on terminal 22.
A quick power down and switch to continuity on the meter told us the n/c contact was u/s and therefore needed replacing.
This job came to my attention to look at because the previous shift had:
Changed 78K1 contactor
Attached a laptop to the s7 plc to read it
Belled out the motor and found nothing wrong.

Not a diagram in sight.
1/2hr later the machine is working using only simple test procedures and an electrical diagram.

Please feel free to add,again this will I hope be more of an aid too less experienced folk.

I'll get some plc stuff up to look at too as the principals are the same.
 
Nice one vaughant. I’ll be honest I don’t like modern A4 drawings where your jumping from page to page, I’d much rather have a big A0 sheet. But that’s my personal choice. As for teaching apprentices there have been times when I’ve been near to throttling them.
Us oldies can be as bad, (not me) the number of times I’ve had the same situation as you. Well we changed that, but it still didn’t work. “How far have you got through the sequence.” They hadn’t even got the drawings out! Just jumping from one guess to the next.

My idea of a drawing.
View attachment 11236
It’s for an auto close OCB. Bits of it may look a bit weird as there’s a lot of CT’s used which are referenced to earth.
 
That drawing is fairly clear as to what is what Tony, I have had to build stuff similar to this and Vaughants diagram above, with far more cryptic drawings than either of these.
 
I agree with both of you though wrt to playing guessing games, the only way educated guessing sometimes works, is if you know by experience a particular component is prone to failure.

When I was shown the ropes, I was taught to stop and think first, about what is not happening, and what is happening, this can rule quite a large section of the circuit out, and give a clue to where the problem is likely to lie, or at which stage.

I was also shown how to hit a stage> miss a stage, and only stepping back one step when something is abnormal/un-expected. This can cut the amount of testing by half, but this can sometimes be difficult when you have multiple feedback paths or outputs of one section affecting inputs of another giving misleading results, or if there are multiple faults.

One thing is guaranteed, which ever end of the Fault chain you start at, the fault will lie at the other end!
 
Last edited:
The problem comes when you go looking for drawings and they're missing! Or as we usually find, the drawings are so old they're no longer relevant!
 
@vaughant; this is something I will be covering with our apprentice and you have explained it well.

@sjj84 and RoB2; missing, incomplete, poor drawings is my pet hate. When I do a project I like to trace out what we have, cross-reference with the schematics if we have them then modify to complete. I then like to upgrade the schematics in... wait for it... MSWord... or AutoCAD if I can be bothered! I know for a fact that recent in-house projects in work have been done without the provision of schematics. How can you create a control system with no schematics?

About 9 years ago, because I'd done a course in CAD I was asked to upgrade some schematcs that were over twenty years old with pencilled-in changes/upgrades with supplementary smoke-packet sketches. These are a sample I provided (kept in the original format)...
View attachment SVK10.pdfView attachment SVK05.pdfView attachment SVK09.pdf

Must agree that the German stuff is very organised and keeps you on your toes!

To be good at schemtic reading you do have to put some effort in and practice on different formats.
 
I think you are touching on the fundamental problem in our industry. Its not the apprentices fault per-se, but what training have they actually had and are we attracting the cream of our profession.
I don't know what the answer is and i can understand " management" using a "have a go" approach, what choice do they have? The skills are not there.
Persoanlly i don't like going anywhere near control without a drawing at least to work with, not overly stressed if its not perfect but at least it enables me to find my way around.
Good news is, decent control sparks will always be in demand
 
Having done some major alterations to a control system I gave the drawings to our engineering manager to have updated. They sat on his desk for over a fortnight. So on my shift the machine packs up, and the fault is somewhere in the stuff I’d altered. Now I have a good(ish) memory, but I can’t remember everything I’ve altered. I was having to do the hand over hand method of following each line. I’d all ready done the usual “that can be dodgy” bit and drawn a blank.

Enter the production manager in Attila the Hun mode. “Where the hell are the drawings?” I told him, not 10 minutes he returned with my original drawings. Fault sorted we walked back towards the workshop. As we passed the office block he asked me to go in to the offices. I was sat on the floor howling with laughter, tears rolling down my face. He’d only taken a sledgehammer to the engineering managers door to get to the drawing for me.

Strange thing is, when I returned the next night there was three full sets of drawings waiting for me. My spy in the management morning meeting reported back that the engineering manager was squirming as two of the directors laid in to him. It was only a minor breakdown but it cost about £36K in production.
 
can i just start by saying that when you are an apprentice that you are only as good as the people that train you ,,, you can only learn so much at college or tech the rest is learn or not learned on the job..... Employers need to invest more time and money into proper training of there apprentices.....
 
can i just start by saying that when you are an apprentice that you are only as good as the people that train you ,,, you can only learn so much at college or tech the rest is learn or not learned on the job..... Employers need to invest more time and money into proper training of there apprentices.....

The apprentices need to invest some of their own time as well, I don't believe that everything must be put on a plate and it's some one else's fault that education is lacking. It is easier to nurture apprentices with the right attitude than force feed the disinterested ones.

This is a side of the industry that to a lot is gobbledegook but being able to read drawings and schematics can save a lot of downtime it is too easy now to connect a laptop and expect it to lead you to the fault or reset the faults and wait for it to occur again.
 
There’s two sides to every coin.
How many put the effort in to learn how to read a drawing? It would seem now it’s something that doesn’t add to getting your precious bit of paper at collage so not important. Let loose in the big bad world of industrial electrical it’s what keeps you afloat. In the middle of the night you have a lifeline in the drawings, if you can read them.
I’ve been lumbered with more than my fair share of those who can’t. I’m not just referring to ex apprentices, I’ve had university graduates and time served tradesmen lost on some of the most basic things.

One thing I will add, to understand a drawing you need to know the production process. If you don’t know what a machine is supposed to do you don’t stand a chance.
 
Nice one vaughant. I’ll be honest I don’t like modern A4 drawings where your jumping from page to page, I’d much rather have a big A0 sheet. But that’s my personal choice. As for teaching apprentices there have been times when I’ve been near to throttling them.
Us oldies can be as bad, (not me) the number of times I’ve had the same situation as you. Well we changed that, but it still didn’t work. “How far have you got through the sequence.” They hadn’t even got the drawings out! Just jumping from one guess to the next.

My idea of a drawing.
View attachment 11236
It’s for an auto close OCB. Bits of it may look a bit weird as there’s a lot of CT’s used which are referenced to earth.

Like you Tony, i dislike the A4 format for schematic drawings that can be 30 sheets or more in a book format. You are literary sent all over these 30 sheets tracing out a particular line...
I was trained using full format drawings on a roll, unseen these day's but you could see where you were going, and the the overall picture most of the time.

I would hate to think how many A4 books of schematic sheets you would need on some of the panels i used to work on!!! Eg, ....Think of a panel 12m long 2 m high and absolutely packed solid full of relay's, most of them being latch/unlatch relays along with contactors and god knows what else. ..lol!! The schematic drawings for this panel was on a full size drawing roll with 14 or more sheets, one drawing for each panel cubicle, and 2 or more sheets with external sections where the controls integrated with other control panels!!! lol!!

To be honest, i can't remember being taught how to read schematic drawings at collage, maybe some very basic stuff, but that was about all. All my training on this side of our industry, was given by the companies own training school/collage by lecturers that knew there business, many being retired foreman from the shop floor maintenance sections. And of course, on the job training, with experienced maintenance electricians.

Even with all the training we were given, the were always those that just couldn't grasp the full potential of fault finding with the aid of schematic drawings, they got by, but only just!! lol!!!

Reviewing control panel schematic drawings using these German style A4 sheets is a nightmare for me these days, flicking backwards and forwards between sheets. ...lol!!
 
Last edited by a moderator:
can i just start by saying that when you are an apprentice that you are only as good as the people that train you ,,, you can only learn so much at college or tech the rest is learn or not learned on the job..... Employers need to invest more time and money into proper training of there apprentices.....

I tend to agree with this. My apprenticeship was largely a waste of time, pretty much soley being used as cheap labour for installation work. Now I struggle with some of the fault finding as I never gained the experience and it wasn't through lack of interest on my part.

The majority of the sparks where I work don't bother looking for drawings as they know they're out of date or missing, unfortunately the management couldn't care less as it's not them that'll be struggling in the middle of the night to sort out any problems.

Oh and I agree about the A4 drawings, the majority of ours are on massive sheets, granted they're mostly useless, but it's much easier to work through a circuit when it's all in front of you rather than flicking here and there all the time.
 
Last edited by a moderator:
Just found this lurking on my PC
View attachment 11268
Part of a conveyor sysyem. There would be 10 times this on an A0 sheet.

I should point out. the wiring shown in purple is external to the MCC panel

 
Last edited by a moderator:
All the apprentices we've had over the past few years have had the same problem. Expecting everything on a plate. In fact in 5 years only one out of 20-30 has gone out of his way to learn more, and because of that fact he's now being given opertunitys above anything we've ever given. Rant over lol.
 
My experience of reading and understanding wiring diagrams has mostly come from my day to day work in industry, i cant say I really learnt much at collage apart from the basic circuits. In my opinion you only get out what you put in! In other words you need to help yourself by getting involved and show willing to learn by getting involved in faults that arise. I suppose I was lucky when I was training because I had good guys around me that were willing to stand back and let me take over, but would help when I was struggling. Im nearly 5 years out of my time now, I dont consider myself to be the best maintenance electrician by far but what I have learnt on the job so far will hopefully give me a good grounding to improve on in the rest of my career. I also agree with having drawings on a larger print alot of the new panels were I working are are A3 which I suppose is better than A4!
 
The way I look at it whether they are A4, A3, A1 or A0 any size of schematic diagram is better than none at all when some one is breathing down your neck and the pressure is on

With regard to learning to read schematic diagrams at college we were given practical assignments and had to draw out the schematic before building the circuit on a board and proving it worked, understanding how the diagrams are constructed is half the battle when it comes to reading them
 
Drive references,
All the panels I worked on once we got rid on the open slate panels would be draw out starters. We would keep spares of these to hand. If you couldn’t repair a draw in situ you would get a spare and fit that. The internal wiring was numbered the same be it a 0.5HP drive or 150HP. Bigger drives were hard wired in the cubical.
View attachment 11273
It was the cubical that had the drive reference. I worked on kilns so the first reference would be the kiln number. Second reference the tier in the panel working from the left (a letter). Third reference was the cubical number from the top.
So for a cubical on kiln 2, 3[SUP]rd[/SUP] tier, 4[SUP]th[/SUP] cubical down the reference would be K2/C/4/ followed by the wire number.
View attachment 11274
 
Some great replies as usual.
I certainly wasn't trying to slate apprentices in anyway,I'm just wondering if this is/was common practice to not put such an emphasis on drawings as on my apprenticeship we basically spent 2 years learning control circuits from diagrams,we would get or produce our own diagram,wire it on an old panel in the workshop,swap round and do a maintenance check on the panel that everything was in place,cable numbers,terminals tight etc then rectify any faults and leave the room.
Then the instructors would put various faults on and you were on your own then to find them,90 minutes for 3 faults,some were obvious like a wire out of say L1 to a motor so it turned slow and tripped but some could be really sneaky buggers and snip a return wire within trunking or remove the coil from a relay,sneaky stuff!!!
But it was good and very beneficial,I probably didn't feel that at the time but looking back I can see how great the training was and I'm glad I made it through.
I suppose that's the point of this thread,not to show how clever we are(or not in my case!!!) but to perhaps help others who may not have done a lot of this and spent most of their time looking at the "sparkies arse" while he fixes it and just tells them what it is afterwards,not much learning involved there.

To those who say there aren't good schematics where they work I feel your pain,theres a bad culture where I am of "he knows,ask him" not "there's the diagram,have a look" and also "that was changed 10 years ago,don't you remember?" not when I've been here a year no!!!

However the only way we can improve it is to be a bit more proactive,perhaps sketch it out one day when your free,even a basic drawing,or check who made alterations and see where it's documented,it usually is somewhere (usually obscure!!!).

I'll try getting some PLC diagrams up for the less familiar and a few explanations of how it all works.
 
All the apprentices we've had over the past few years have had the same problem. Expecting everything on a plate. In fact in 5 years only one out of 20-30 has gone out of his way to learn more, and because of that fact he's now being given opertunitys above anything we've ever given. Rant over lol.
i can honestly say when i was an apprentice i went the extra mile as far as im concerned .... i love being a aspark and take real pride in my work.....
iknow the type of folk ya on about and they don't usually make good sparks just do enough to get by.....
but i stand by what i said some of the fellas that ive herad about in past cannot be arsed with it or have been to busy to train properly........
so it a double sided edge.......
 
i can honestly say when i was an apprentice i went the extra mile as far as im concerned .... i love being a aspark and take real pride in my work.....
iknow the type of folk ya on about and they don't usually make good sparks just do enough to get by.....
but i stand by what i said some of the fellas that ive herad about in past cannot be arsed with it or have been to busy to train properly........
so it a double sided edge.......

It's not only those that can't be arsed as you say..lol!! Some just don't have the aptitude for this kind of work, they just can't get there head around it. I've known some dammed good electricians and Engineers come to that, who just can't fault find process control circuitry. So it's not always just the lack of trying, but i agree with you, some are happy to just do enough to get by.
 
It's not only those that can't be arsed as you say..lol!! Some just don't have the aptitude for this kind of work, they just can't get there head around it. I've known some dammed good electricians and Engineers come to that, who just can't fault find process control circuitry. So it's not always just the lack of trying, but i agree with you, some are happy to just do enough to get by.
:plol,,lol,,, i was on about the guys who sometimes et left to teach the new apprenices ,,, not the lads ho wanna be sparks.......the psarkies who choose or a choosen to teach the new lads should have to do a course of somekind to see if they have the right attitude and aptitude and pacience for the job in hand .... ya could be the best sparkie in the world but ya may not be able to teach others .......lol.......
 
Some great replies as usual.
I certainly wasn't trying to slate apprentices in anyway,I'm just wondering if this is/was common practice to not put such an emphasis on drawings as on my apprenticeship we basically spent 2 years learning control circuits from diagrams,we would get or produce our own diagram,wire it on an old panel in the workshop,swap round and do a maintenance check on the panel that everything was in place,cable numbers,terminals tight etc then rectify any faults and leave the room.
Then the instructors would put various faults on and you were on your own then to find them,90 minutes for 3 faults,some were obvious like a wire out of say L1 to a motor so it turned slow and tripped but some could be really sneaky buggers and snip a return wire within trunking or remove the coil from a relay,sneaky stuff!!!
But it was good and very beneficial,I probably didn't feel that at the time but looking back I can see how great the training was and I'm glad I made it through.
I suppose that's the point of this thread,not to show how clever we are(or not in my case!!!) but to perhaps help others who may not have done a lot of this and spent most of their time looking at the "sparkies arse" while he fixes it and just tells them what it is afterwards,not much learning involved there.

To those who say there aren't good schematics where they work I feel your pain,theres a bad culture where I am of "he knows,ask him" not "there's the diagram,have a look" and also "that was changed 10 years ago,don't you remember?" not when I've been here a year no!!!

However the only way we can improve it is to be a bit more proactive,perhaps sketch it out one day when your free,even a basic drawing,or check who made alterations and see where it's documented,it usually is somewhere (usually obscure!!!).

I'll try getting some PLC diagrams up for the less familiar and a few explanations of how it all works.
iknow i have not had 2 years training looking at drawings , the old apprentice schemes were maybe more thorough than today.... i don't know.... everything seems to be fast track now........ or ya have to do another course to do be trained to read drawings ect , which meens more cash to be piad to get the said qualification......it never ends went ya a spark.....
 
:plol,,lol,,, i was on about the guys who sometimes et left to teach the new apprenices ,,, not the lads ho wanna be sparks.......the psarkies who choose or a choosen to teach the new lads should have to do a course of somekind to see if they have the right attitude and aptitude and pacience for the job in hand .... ya could be the best sparkie in the world but ya may not be able to teach others .......lol.......

Sorry, ...Miss read your post it seems...lol!!
 
:plol,,lol,,, i was on about the guys who sometimes et left to teach the new apprenices ,,, not the lads ho wanna be sparks.......the psarkies who choose or a choosen to teach the new lads should have to do a course of somekind to see if they have the right attitude and aptitude and pacience for the job in hand .... ya could be the best sparkie in the world but ya may not be able to teach others .......lol.......

Yep, I whole heartily agree. The other problem is that management are constantly on the backs of the sparks that are trying to teach to get machines working again. If the spark has been there a long time, they may well have seen the fault before, so rather than fault finding or using drawings, they go straight to the fault rather than allowing the apprentices to get stuck in and have a go. It's a difficult one really, apprentices need guidance, not having it handed on a plate, but sometimes that opportunity just isn't given.
 
Yep, I whole heartily agree. The other problem is that management are constantly on the backs of the sparks that are trying to teach to get machines working again. If the spark has been there a long time, they may well have seen the fault before, so rather than fault finding or using drawings, they go straight to the fault rather than allowing the apprentices to get stuck in and have a go. It's a difficult one really, apprentices need guidance, not having it handed on a plate, but sometimes that opportunity just isn't given.

That is the other side of fault finding were certain faults are recurring ones and are just fixed using previous knowledge and experience
 

Reply to Electrical Diagrams in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock