Discuss Expanding off self grounding outlet in the DIY Electrical Advice area at ElectriciansForums.net

Baldar538

DIY
Reaction score
0
Hi - I'm trying to add an additional outlet to a circuit in my house. I tested the outlet with a tester, and it showed as correct. The existing outlet is facing the finished part of the basement, but where I am looking to add an outlet is in the unfinished utility room behind the wall. I have full access to the box and everything I need back there, but due to it being unfinished I have to use MC, AC or metal conduit, I can't just use Romex right? The path this needs to take would be easy for MC, but would be a pain to run conduit around for what it's worth.

When I opened up the box though I noticed there was only a hot and a neutral going to the outlet. Since it is passing an outlet test, I'm assuming that it's a self grounding outlet?

I had already swung by Home Depot and picked up a https://www.homedepot.com/p/Southwi...-Assembly-Quick-Cable-Whip-56482401/204804403 for use in the project. As this is MC the sheath cannot be used as ground, correct? I would have to use the green ground wire inside of it?

As the existing outlet doesn't have anything to pigtail on to, yet is grounded, what would be the correct way to wire this?

So - given a box with a two wire outlet which is passing a test for ground what would be the best way to wire one more outlet in the circuit? Because it's passing a test for ground, do I pick up some ground wires like https://www.homedepot.com/p/Commerc...ls-with-Screws-Green-5-Pack-GP128-5/310747594 and attach it to the existing box, then pigtail in both the existing outlet and the green wire from the MC? On the new outlet end of things I would just connect that ground to the green screw on the new outlets and not to the box as the MC sheath isn't a ground path?
 
TL;DR
Existing outlet two wires yet has a ground path. Bought MC cable to extend circuit to a new outlet in unfinished area. Trying to figure out how to wire maintaining good ground path.
Hi - I'm trying to add an additional outlet to a circuit in my house. I tested the outlet with a tester, and it showed as correct. The existing outlet is facing the finished part of the basement, but where I am looking to add an outlet is in the unfinished utility room behind the wall. I have full access to the box and everything I need back there, but due to it being unfinished I have to use MC, AC or metal conduit, I can't just use Romex right? The path this needs to take would be easy for MC, but would be a pain to run conduit around for what it's worth.

When I opened up the box though I noticed there was only a hot and a neutral going to the outlet. Since it is passing an outlet test, I'm assuming that it's a self grounding outlet?

I had already swung by Home Depot and picked up a https://www.homedepot.com/p/Southwi...-Assembly-Quick-Cable-Whip-56482401/204804403 for use in the project. As this is MC the sheath cannot be used as ground, correct? I would have to use the green ground wire inside of it?

As the existing outlet doesn't have anything to pigtail on to, yet is grounded, what would be the correct way to wire this?

So - given a box with a two wire outlet which is passing a test for ground what would be the best way to wire one more outlet in the circuit? Because it's passing a test for ground, do I pick up some ground wires like https://www.homedepot.com/p/Commerc...ls-with-Screws-Green-5-Pack-GP128-5/310747594 and attach it to the existing box, then pigtail in both the existing outlet and the green wire from the MC? On the new outlet end of things I would just connect that ground to the green screw on the new outlets and not to the box as the MC sheath isn't a ground path?
Uploading pictures for context. Two of the outlet that passes a ground test but only has two wires.

The other picture is the back of that outlet and part of the path I'm looking to run the new outlet. It should be headed in a similar direction as that piece of coax on the right heading towards me while taking the picture.

(And there were probably better ways to run that conduit in the picture, but that's the previous owners handiwork not mine - maybe someday I'll get to the point it bothers me enough to fix it)
 

Attachments

  • IMG_3104.jpeg
    344.6 KB · Views: 6
  • IMG_3103.jpeg
    327.9 KB · Views: 6
  • IMG_3100.jpeg
    419.8 KB · Views: 6

Reply to Expanding off self grounding outlet in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
622
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
466
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
812
I had done this about 30 years ago, and, IIRC, it was a series of boxes, Romex coming in, and Romex coming out, one in, one out, each box, except...
Replies
3
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock