Discuss Exporting the earth? in the Electricians' Talk area at ElectriciansForums.net

Antimatter,
can I ask then, if you are installing outside lights or sockets wired to the main building which is on a TNCS....do you rod them individually,and separate the earth....or use the TNCS?....I ask because logically if you are so appalled by the thought of a shed on a TNCS then presumably you feel the same about an outside light?.....if not why not?

The best example is the outside socket, used exclusively in the main for garden tools and the like.... If there is a possibility of RISK, then surely this is the best example of how ludicrous some of these objections are!!!
 
The best example is the outside socket, used exclusively in the main for garden tools and the like.... If there is a possibility of RISK, then surely this is the best example of how ludicrous some of these objections are!!!

Outside light has the CPC connected to the MET, if extraneous metalwork in an outbuilding can introduce an earth potential within the installation.
 
Outside light has the CPC connected to the MET, if extraneous metalwork in an outbuilding can introduce an earth potential within the installation.



I think you are a wind-up, either that or you haven't bothered to read any of the posts that don't agree with your very confused version of the Reg's, ....or come to that ''common sense''
 
Straight from the IET FORUM

The inspector has asked for a metal shipping container cabin housing a db for a soil washer to be made into a TT as the supply is a TNCS pme .Now i understand you cant export PME but the feed for this db comes from another metal cabinet which in turn is fed from a metal shed all pme .

so is this user on the IET forum wrong as well chaps? or do you want me to post more examples?
 
I think you are a wind-up, either that or you haven't bothered to read any of the posts that don't agree with your very confused version of the Reg's, ....or come to that ''common sense''

I think the main concern is the danger associated with differences in earth potential in the event of a supply neutral fault.
 
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
 
Straight from the IET FORUM

The inspector has asked for a metal shipping container cabin housing a db for a soil washer to be made into a TT as the supply is a TNCS pme .Now i understand you cant export PME but the feed for this db comes from another metal cabinet which in turn is fed from a metal shed all pme .

so is this user on the IET forum wrong as well chaps? or do you want me to post more examples?


If you bothered to read the rest of the thread that you copied & pasted that post from, you would see that they infact agree that PME can be exported to an outbuilding!!!!!!!!!
 
Unless you can provide details of distance from the supply point to this container, there is no possibility to agree or disagree. But it does go to show that the PME has been as you call it ''exported'' before it even got to this container....
 
Broken neutral conductor

The neutral of a supply is often common to a large number of installations. In the (unlikely) event of a broken neutral, all the consumers on the load side of the break could have a combined neutral and earth potential of the same level as the phase system (240 V to earth). This situation could be very dangerous, because all earthed metalwork would be at 240 V above the potential of the general mass of earth.

To prevent such an event, the Electricity Supply Company connects its combined neutral and earth conductor to earth electrodes at frequent intervals along its run. Whilst this does not entirely remove the danger, it is much reduced. For example, the assumed earth resistance values show that the maximum possible potential to earth in this case would be 96 V. In practice, much lower resistance values for the earth connections will reduce this voltage. The Electricity Supply Company goes to very great lengths to ensure the integrity of its neutral conductor.

http://www.tlc-direct.co.uk/Book/5.6.3.htm
 
Special requirements PME-fed installations

An installation connected to a protective multiple earth supply is subject to special requirements concerning the size of earthing and bonding leads, which are generally larger in cross-section than those for installations fed by supplies with other types of earthing. Full discussions with the Electricity Supply Company are necessary before commencing such an installation to ensure that their needs will be satisfied. The cross-sectional area of the equipotential bonding conductor is related to that of the neutral conductor as shown in {Table 5.9}Table 5.9 - Minimum cross-sectional area of main equipotential

----------------- bonding conductor for PME-fed installations
Neutral conductor c.s.a. (mm²) Main equipotential bonding conductor c.s.a (mm²)
35 or less 10
Over 35 and up to 50 16
Over 50 and up to 95 25


Danger can arise when the non-current carrying metalwork of an installation is connected to the neutral, as is the case with a PME-fed system. The earth system is effectively in parallel with the neutral, and will thus share the normal neutral current. This current will not only be that drawn by the installation itself, but may also be part of the neutral current of neighbouring installations.

It follows that the earth system for an installation may carry significant current (of the order of tens of amperes) even when the main supply to that installation is switched off. This could clearly cause a hazard if a potentially explosive part of an installation, such as a petrol storage tank, were the effective earth electrode for part of the neutral current of a number of installations. For this reason, the Health and Safety Executive has banned the use of PME in supplies for petrol filling stations. Such installations must be fed from TN-S supply systems (RSE booklet RS(C)41
- 'Petrol Filling Stations: Construction and Operation').
 
Last edited by a moderator:
And remember electricians, don't have nightmares, have nice dreams about a PME earthing system with an outbuilding with extraneous metalwork that is connected to an earth electrode.

zzzzzzzzz zzzzzzzzzzz
 
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.

This situation could be very dangerous, because all earthed metalwork would be at 240 V above the potential of the general mass of earth.

Common - not, Dangerous - very.

Do you want to take that chance? its your name on the paperwork, not mine.
 
This situation could be very dangerous, because all earthed metalwork would be at 240 V above the potential of the general mass of earth.

Common - not, Dangerous - very.

Do you want to take that chance? its your name on the paperwork, not mine.

Which is why equipotential bonding is very important, providing the installation has an RCD and the above happens, and all equipotential bonding is in place and resistance is 1667ohms or lower the RCD will operate.
 
Which is why equipotential bonding is very important, providing the installation has an RCD and the above happens, and all equipotential bonding is in place and resistance is 1667ohms or lower the RCD will operate.

Do you mean supplementary bonding conductors?

Equi-potential is 16th Edition terminology and if used in an exam, would result in a fail.

Source
Chied Examiner - City and Guilds
 
Every time I read of the mass deaths from broken supply neutrals on exported TN-C-S system, I will think of you.

You should contact BBC Watchdog with your findings, you are a national hero of electrical engineering and I am turning to landscape gardening to contemplate my ignorance.
 
Every time I read of the mass deaths from broken supply neutrals on exported TN-C-S system, I will think of you.

You should contact BBC Watchdog with your findings, you are a national hero of electrical engineering and I am turning to landscape gardening to contemplate my ignorance.

as you say Do it once, do it right....
 
Ahhhh, the sweet sounds of defeat, i knew i was right all along :)

Its true that persistence really does pay off

The above quote is neither helpful nor constructive. I for one have a great deal of respect for members on here like Lenny who have given a great deal of their time to this forum unpaid and all they ask for is the curtiousy of the thanks button being hit every now and then.
 
antimatter shhhhhhhhhhhhhhhhhhhhhhhhh!

please respect your elders because the will now a hell of a lot more than you!!!
there is so many blokes on here just trying to help and from what i see all you want to do is cause problems!!!

danny
 
Last edited by a moderator:
I believe the correct term as used in BS7671 (17th edition) is Supplementary Equipotential Bonding. This is a method for providing additional protection.
That aside, there is no regulation in BS7671 or ESQCR that prohibits the exportation of a PME earth.
Individual DNOs can and do put restraints on where and to what they will allow connection to their PME system, but that is their choice, not something contained in any standard or statutory document.
There are prohibitions on providing a connection to a PME system for caravans, petrol stations and marinas, obviously exporting a PME earth in such situations would also be prohibited.
The thread from the IET forum you quoted concerned a mobile shipping container, these are often treated the same as caravans. The OP in that thread erroneously believed that a PME earth cannot be exported, hopefully he went away eductaed to the fact that it can be.
One of the problems with exporting a PME earth to an outbuilding containing extraneous parts, is that those parts may well be at a differnt potential to earth than the exported earth. The use of protective bonding will equalise any potential difference, but an appropriately sized protective bonding conductor back to the point of supply will have to be installed.
Often it is more cost effective not to export the earth, and to TT the out building.
 
antimatter shhhhhhhhhhhhhhhhhhhhhhhhh!

please respect your elders because the will now a hell of a lot more than you!!!
there is so many blokes on here just trying to help and from what i see all you want to do is cause problems!!!

danny

Because my interpretation of the regs is different from other peoples doesn't mean that im causing problems at all, on the contrary, it is others if you read the earlier posts who are derogatory to me, please read the posts back, this is a forum not a text book, and different people have different opinions danny
 
im not saying its a text book, all im saying is iv been on here and needed advice regarding all sorts and someone has help me, the people that have helped me you seem to be having a problem with. imo everyone has there own opinion which is fine but please respect the member on here!!!

danny
 
im not saying its a text book, all im saying is iv been on here and needed advice regarding all sorts and someone has help me, the people that have helped me you seem to be having a problem with. imo everyone has there own opinion which is fine but please respect the member on here!!!

danny

Why do you think people have a problem with me?
 
Because my interpretation of the regs is different from other peoples doesn't mean that im causing problems at all, on the contrary, it is others if you read the earlier posts who are derogatory to me, please read the posts back, this is a forum not a text book, and different people have different opinions danny

The problem was never about your opinion, as you say you are entitled to it. It was the fact that at the start of this thread you told the op that they can not export a tncs earth. You did not state this as your opinion, you stated it as fact. Which it is not.
 
The problem was never about your opinion, as you say you are entitled to it. It was the fact that at the start of this thread you told the op that they can not export a tncs earth. You did not state this as your opinion, you stated it as fact. Which it is not.

An opinion is a fact of the person sending the message as a fact, which is his opinion is correct.
 
This thread is closed and i will not say it again and that includes private messages being sent to other members regarding it. enough has been said and this is an end to it.
 

Reply to Exporting the earth? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
530
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock