Just had three split Air Con units installed at my home, the ones with an indoor and outdoor unit.

I (perhaps naively) trusted the installers when they said they could tap into the existing socket ring to power them. I had assumed they meant installing a couple of fused spurs.

What I've ended up with is 1.5mm SY cable shoved through the wall into the back of a socket in two places. One goes to one outdoor unit, the other goes to two, both via rotary isolators. Obviously the SY cable hasn't been properly terminated indoors.

So I'm not hugely happy about the safety or compliance of this. Problems I can see:

1. SY cable shouldn't be used like this
2. Running two fixed appliances from one unfused spur
3. Attaching 1.5mm cable to a 2.5mm ring with no fuse protection

I could get a spark to sort it but I'm wondering if there's anything I could do myself to bring this into compliance.

My initial idea would be to remove the SY cable from where it's connected, and properly connect it instead to a 13-amp FCU which I could install next to the existing socket. Then I could power the FCU as a spur from the socket. This would have the advantage of giving an internal way to disconnect the AC if required since the outside rotary switches aren't very accessible. Alternatively, I could see if I could remove the SY cable all the way to the rotary isolator and replace it with something more appropriate. What do people think?

If it helps the air con units are relatively low powered. Two are 4A operating current and one is 5.6A, so the max load on a spur would be 9.6A on one and 4A on the other.

Any help gratefully received!
 
I think I'd be getting the installers back, or demanding a part refund to be honest.
At the moment I'm not confident enough about how this would be made right, or what rules they are breaking, to tackle them and demand action. If someone can suggest exactly how this should be made compliant? I don't have any faith in them to fix it themselves though, I'd have to know exactly what should he done.
 

Reply to Help with an Air Conditioning install in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K
  • Article
Electrical2Go - Beginners Guide to Positive Input Ventilation (PIV) Units: A Solution to Indoor Air Quality Woes A guide to Positive Input...
Replies
0
Views
242
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
531
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock