I have been asked to provide a quote for a supply to an toilet block on a campsite.
The three phase supply to the campsite is approx. 150m from the mains incoming supply and fed off an 40amp type b mcb. The cable is 35mm 5-core SWA.
The issue I have is when I measured the Zs at the campsite DB it is 0.86 ohms, which is very much on the edge.
I don't want to add any additional circuits because of this.
What are my options to get a better Zs ?
An 30mA rcd at origin would cause issues as there is sub boards, can you earth spike at the campsite DB in addition to the supply earth ? or should I just make every circuit off the campsite an TT supply and earth spike each one ?
The three phase supply to the campsite is approx. 150m from the mains incoming supply and fed off an 40amp type b mcb. The cable is 35mm 5-core SWA.
The issue I have is when I measured the Zs at the campsite DB it is 0.86 ohms, which is very much on the edge.
I don't want to add any additional circuits because of this.
What are my options to get a better Zs ?
An 30mA rcd at origin would cause issues as there is sub boards, can you earth spike at the campsite DB in addition to the supply earth ? or should I just make every circuit off the campsite an TT supply and earth spike each one ?