Search for tools and product advice,

Discuss TT Install with Solar - RCD question in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315
Hello

Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January.

Existing is a TT system with a solar installation fitted.

Current install has a 100A TP incomer, meter, C63 TP MCB, solar install, 100ma RCD, distribution board fitted with more MCBs than there are RCBOs.

Please see photo attached.

I have no experience with solar installations. Am i “allowed” to relocate the enclosures and shorten the tails going to them?

Can these tails be covered by my new proposed 100A 100mA time delay RCD or is there a reason they haven’t already been by the previous installer - something in the regs relating to this maybe?

Proposing to go from the meter to a 100A 100mA switch, then to solar, then to new DB with 30mA protected circuits throughout.

There’s a few three phase circuits but nothing requiring additional protection (cables supply air conditioning and refrigeration condensing units and not hidden within walls, no sockets etc etc) so going to omit the 30mA protection from these.

Look forward to your input.

Thanks
 

Attachments

  • IMG_4816.jpeg
    1.2 MB · Views: 29
Proposing to go from the meter to a 100A 100mA switch, then to solar, then to new DB with 30mA protected circuits throughout.
That sounds perfectly sensible.

I would say to check the solar inverter manufacturer's instructions about the type of RCD that is permitted. If it is fine for type A then no problem in finding one for your "100A 100mA switch" (presumably the delay/selective RCD) before the DB.

If they require a type B then cost is going to be much higher and very few make them, Doepke are the only ones I have noticed by no doubt a few like Schneider and ABB do them for a largely EU market.

There’s a few three phase circuits but nothing requiring additional protection (cables supply air conditioning and refrigeration condensing units and not hidden within walls, no sockets etc etc) so going to omit the 30mA protection from these.
Your issue with doing that is no selectivity - if any of them have a L-E or N-E fault then your incomer will almost certainly trip as it is very unlikely your Ra will be low enough to clear on any MCB's magnetic trip (which is faster than a selective RCD).
 
Last edited:
Thanks for the reply. Noted about omitting the 30mA RCDs, will look at purchasing 4pole 30mA RCDs and a larger enclosure to house those and our proposed SPD.

Do you have experience with those solar energy units? Done a bit of Google’ing and can’t find anything on them. There are 3 of them so potentially 1 per phase but they all look to be connected together as well.

Can’t see any cables coming from them heading to solar panels etc, customer says he doesn’t have solar panels.

Another thought is the possibility of them being battery packs rather than some sort of solar setup?
 
Thanks for the reply. Noted about omitting the 30mA RCDs, will look at purchasing 4pole 30mA RCDs and a larger enclosure to house those and our proposed SPD.
It can be cheaper / simpler to have a DIN box beside the DB for added RCDs than trying to find cost-effective RCBO options for 3P circuits.
Do you have experience with those solar energy units? Done a bit of Google’ing and can’t find anything on them. There are 3 of them so potentially 1 per phase but they all look to be connected together as well.

Can’t see any cables coming from them heading to solar panels etc, customer says he doesn’t have solar panels.

Another thought is the possibility of them being battery packs rather than some sort of solar setup?
I don't see any info in your post or photo, certainly if there are no solar panels it would seem strange! I can't imagine battery packs being of that much use without some for of local generation, beyond your UPS sort of arrangement for keeping computers going.
 
Can these tails be covered by my new proposed 100A 100mA time delay RCD or is there a reason they haven’t already been by the previous installer - something in the regs relating to this maybe?

Solar should not be on the load side of any RCD which is shared with any normal circuit. Hopefully the reason is obvious, although I guess the issue will be reduced if the RCD is for fault protection only.
 
Solar should not be on the load side of any RCD which is shared with any normal circuit. Hopefully the reason is obvious, although I guess the issue will be reduced if the RCD is for fault protection only.
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as additional protection.
 

Reply to TT Install with Solar - RCD question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
988
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock