Search the forum,

Discuss How to carry out PEFC and PSCC on a three phase db with a rcd as the supply? in the UK Electrical Forum area at ElectriciansForums.net

RyanF

-
Reaction score
27
Ive got my am2 resit tommorow for my live testing and I ran out of time and failed as well as I carried out the ze test on 2 lead high thus tripping the rcd.

So now I know for next time to complete this on a 3 lead LOW test and measure ze with earth disconnected etc.. then connect main earth back after the test.

But how would you measure pefc and pscc on the three phase db.

The plan I had was for PEFC:-

Set the megger mft1740 to L-PE on 3 low test and croc on to the main earth first, then probe on the Neutral then the phase.

So I would do :- L1- N- E
L2- N -E
L3 -N-E

Note down the highest value for PEFC.

Then same connections set the tester to L-L/L-N to measure PSCC

Same test points again

L1-N-E
L2-N-E
L3-N-E

Note down the highest value as PSCC.

If meter can measure phase to phase then do the tests. But, if not simply take the highest value and times by 2 or more accurately 1.732.

Then record this value as PFC.

Is this right or should I be doing 2 lead low test, but wont this trip the rcd? I have in my mind to do 3 lead low test to not cause any imbalance in the rcd.

Cheers!
 
What test meter will you be using? Have you Googled the user guide for the test meter?
 
This is the second thread you have opened in a similar vein to the one you started Friday with 47 posts. If you don't know the answer by now another thread is probably not going to help you.
 
On a TT system PEFC won't be the PFC. Only PSCC is relevant, and it is the maximum value between phases that you need (or double the highest phase to neutral value).

Technically a phase to phase to phase fault (i.e. a simultaneous fault between all three phases) will be the worst but we can't measure this.
 
You would never energise an installation with the earthing conductor removed for obvious reasons. The Ze test is done on the supply side of the mainswitch/protective device.
 
Probably too late, so good luck in the test.

You know from the design of the test bay that you have an RCD in circuit at all times and you do not want to trip this therefore whenever you are measuring Zs, Ze, PEFC then use the 3 lead Lo test setting.

For the testing you have access to all conductors and so there is no need to attempt any other method of testing when testing to earth.

You should not need the green lead to earth for the PSCC test, because of the test conditions you should only test between neutral and each phase as it is not considered necessary to test between phases, the highest measured result is multiplied by 2 to give the value to record on the test sheet as PSCC.
 
Yep,i think we sometimes forget,that the test set-up,is different,from most of the actual real test situations,which is a bit disheartening.

That said,an understanding of the testing procedure,means the candidate should not be troubled by this.

I mean,Ze/Zb...potato/tomato...

I reckon we should go back to the days when,for example,you did military basic training,and there was an accepted percentage of fatalities...;)
 

Reply to How to carry out PEFC and PSCC on a three phase db with a rcd as the supply? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock