How to test a circuits in steel conduit as the cpc

Discuss How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Good evening

I am currently a training to become an electrician. I do hold both initial verification and periodic testing qualifications however this is an issue I have never personally had to deal with and was never mentioned on any of my courses as often seems to be the case.

Basically I am wondering how you would hypothetically go about testing either a ring or radial circuit if you didn't have a seperate cpc but the conduit itself acted as this.

Look forward to hopefully getting a response and some clarity

Regards Harry
 
Problem here, is that we work to BS7671, not to the NICEIC regulations.
There are no tables of maximum R1+R2 in BS7671, there are only tables for maximum Zs.
So it’s all very well measuring R1+R2 and adding it to Ze, but what do you do if that value is above the maximum permissible?
Then either the design is wrong or it has not been constructed to the design. A parallel path can be out of the control of the designer and in practice, this could disappear by a plumber inserting a plastic Tee in a copper pipe.
 
In the 17th GN8 amd3 (which is the last GN series I currently have) it gives reg 411.3.2.6 and states "Supplementary bonding is required by BS7671 to be provided in the following circumstances: where, in the event of an Earth fault, the conditions for automatic disconnection cannot be fulfilled in the time required by reg 411.3.2.2, 411.3.2.3 or 411.3.2.4, as appropriate"

The other circumstances listed are in special locations such as bathrooms etc,,, etc.

This sure looks like reducing the Zs to me :)
 
I’ve had that feeling every time I’ve replied to a comment lol. On a serious note I feel that some people who are doing EICRs are not clued up enough to be doing them.
When you've had that feeling as often as I have, over the years, I might take you seriously.;)

As regards your serious note....I totally agree.
 
Just out of (genuine) interest Westy can you give me the reg number for the 16th where SB was not allowed to reduce a Zs ?, I still have regs books and some OSGs going back to the 15th ed and I will look it up.

The special locations bit in my previous post, which I never bothered writing out is more to do with reducing Ut (touch voltages) which is a different kettle of fish entirely.
 
So Ian, are you saying in effect that SB can be used to lower a Zs to achieve disconnection times ?, I do have the 18th regs book but I am just being lazy ;)

I don't have the 18th GNs yet, but I am considering getting them
 
So Ian, are you saying in effect that SB can be used to lower a Zs to achieve disconnection times ?, I do have the 18th regs book but I am just being lazy ;)
Supplementary bonding to the location between accessible exposed conductive parts and extraneous parts and circuits is one method.
Another more commonly used method is Rcd protection
 
There are basically two reasons for SB, the special locations part is to do with reducing Ut to keep it below 50V, medical locations below 25V, back in the 16th agricultural locations required Ut below 25V as well I recall, but I don't recall now which specific amd, or if it ever changed in that entire edition.
The other part is to achieve disconnection times and was to reduce Zs by default, the regs are worded --- backward in a lot of cases.
 
There are basically two reasons for SB, the special locations part is to do with reducing Ut to keep it below 50V, medical locations below 25V, back in the 16th agricultural locations required Ut below 25V as well I recall, but I don't recall now which specific amd, or if it ever changed in that entire edition.
The other part is to achieve disconnection times and was to reduce Zs by default, the regs are worded --- backward in a lot of cases.
I can’t even remember the 16th that well
Wish I had kept my yellow copy I used to pass the exam.
What I do remember from that time is the awful bonding and in particular the radiator clamps we used to supplementary bond the bathrooms
Looked hideous if you couldn’t hide them
 
No, I could get my 16th editions out, but as the disconnection times part are still in the current edition and GN8 for the 17th amd 3 there is not much point really, I will look up the regs spin posted up later, and see what actually changed.
 
So I have been in the loft and after looking for a red book realised I had a blue hard back copy.
20190302_185500.jpg
 
This is the latest version:
419.3 Except where Regulation 419.2 applies, if automatic disconnection cannot be achieved in the time required by Regulation 411.3.2.2, 411.3.2.3 or 411.3.2.4 as appropriate, supplementary protective equipotential bonding shall be provided in accordance with Regulation 415.2 and the voltage between simultaneously accessible exposed-conductive-parts and/or extraneous-conductive-parts shall not exceed 50 V AC or 120 V DC.
 
In the brown book 16th 413-02-15 is deleted in 1992 amd2

This reg is present in the green book amd1: 1992 16th though, and says pretty much the same as the blue book above (which I also have).

The 16th was a bit strange as there was at least one reset in between the green book amd 1 :1992, the blue book :2001 (no amd given even though it is almost a decade later) and the brown book :2004 both amd 1+2

brown book 16th.jpg


green book 16th.jpg
 

Reply to How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net