Discuss LED drivers (DALI) regulary fail in the Lighting Forum area at ElectriciansForums.net

Emile

-
Reaction score
0
In a new building about 400 TCI LED drivers of type 122692 were installed. This concerns DALI drivers.
The vast majority of these drivers are in a dimmable setup (DALI).
The problem now is that drivers regularly fail. In itself not the end of the world, but there is the programming costs every time.
In the building there are other LED lamps, the drivers of those lamps are not going defect. For the rest there are no problems with other devices in the building.
....
TCI is of the opinion that the defects are due to overvoltage.
I think this explanation is actually insufficient, because if there is overvoltage in the building, other devices should also go defect.

Does anyone have ideas?
 
love his paintings, but would not trust him with electrical equipment.seeing his experiment with starfish dimming, doesn't instill a lot of confidence.

175_dali04.jpg
 
First off did you get certification from the various manufacturers as to the compatability of the components of the system. Who designed and installed the system? IF...overvoltage is the problem, which I doubt you should get a monitor (power quality analyser) to check any anomalies in the supply to present as evidence this is not the case. You say you have four hundred control gears? The inrush current must be immense. Are you talking about a particular section of the building where it is all failing or generally around the building? In any event it may be that components in the control gear are poor quality. There are a few methods of dimming in led control systems has all this been considered?
 
As per previous comments. What is the voltage? Has it been tested? If above 247v or lots of high fluctuations that could be reason for drivers failing. Suggest add SPD and if funds will allow put lighting on UPS without batteries to clean supply. But before doing anything check to see how dirty the supply is with an analyser as that will give you confidence as what to do next.
 
Easiest is to try a small number of say Tridonic drivers. If you start chasing the supply voltage you could be there a long time .
I have had a good 50% of failed Osram drivers, also i have had drivers that "shutdown" they looked faulty but simply needed a 30 minute power off cycle, bizarre, this was caused by brown outs. I had to advised the client to switch off lights for 30 minutes. These TCI drivers look to have very similar protection circuitry which i believe is microprocessor controlled, the ones i had were sensitive to undervoltage , it caused them to get confused.
 
https://win.tcisaronno.com/downloads/?IDnode=1168&field=docs

The TCI LED drivers of type 122692 has a rated output for an ambient temperature ta from -25 to 45 C and case temperature of tc of 75C. They also have integral thermal protection to automatically shut down before damage from overheating. Are they located somewhere without sufficient ventilation? Perhaps buy a few max/min thermometers and attach some to the drivers and hang a few others up to measure the surrounding air temperature.

Large Digital Max Min Thermometer - White 12/426/3 | Brannan - https://www.brannan.co.uk/large-digital-max-min-thermometer-white
 

Reply to LED drivers (DALI) regulary fail in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hey folks, i work for a relatively small company, but we are doing some big jobs. And right our headache is taking over outdoor lighting...
Replies
4
Views
1K
This is just a note about LED bulb failure. We had a desk lamp in which the A19 LED bulb would only go on after flipping the switch several times...
Replies
6
Views
959
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
812
So picuture under cabinet lights, a 230 supply from a spur, to a LED tamlite driver, and 2 lights coming off of this... why is it that one of the...
Replies
5
Views
1K
My view on life, in any field, is not to produce more but to consume less. Everybody told me this is a very eccentric weird mentality. Perhaps...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock