evening guys, ive come across lighting in one room of domestic premises that has been supplied from the ring main at some point. the cable coming from the ring is 1,5mm which goes through the switch then on to the 2 x 12V down lights. This is on an EICR I`m doing. There is no chance at all of accessing under the floor boards as there is very expensive oak flooring down every where. I believe that from memory you can use a switched fused spur for functional switching. I could then put in a 5A fuse and the load side of the cable will be protected. My concern though is the piece of 1,5mm from ring to switch? your thoughts on this would be welcome. I see this as no different to taking a spur off the ring for an extra socket etc, or am I forgetting some thing?
 
yes nothing wrong with spurring down lighting circuit of ring main. ( bad circuit design). But that 1.5mm cable needs to be replaced to 2.5mm to feed side of spur
 
I agree with what you are saying Dave, its for sure bad practice but from a technical point of view that 1,5mm supply to fused spur is inaccessible so no chance of to many amps being pulled through it.
 
David...
whats the minimum CSA for FCU feeds?
and given that the largest fuse to BS1362 (13A) is under the max CCC of a 1.5/1.0 flat twin....
the fuse will dictate Max demand here so...

Yes Glen I take your point that FCU aint gonnar pull more than 13amp tops (max) or min 1amp depending what size fuse you put in so yes it will dictate max demand.But its just bad practice to have that size cable.
 
Yes Glen I take your point that FCU aint gonnar pull more than 13amp tops (max) or min 1amp depending what size fuse you put in so yes it will dictate max demand.But its just bad practice to have that size cable.
David...
you need to rethink statements like this ...as they are misleading to the pups in here...
 
Because its not the way we usually do it does not make it bad practice.
As stated above the FCU protects the 1.5 against overload. The MCB will still give adequate fault protection (Zs being correct of course!)
 
Could you not fit a fcu with 5a fuse in it next to the socket the 1.5mm is coming from and put the 1.5mm on the load side and a bit of 2.5mm between the socket and fcu next to it.
 
Could you not fit a fcu with 5a fuse in it next to the socket the 1.5mm is coming from and put the 1.5mm on the load side and a bit of 2.5mm between the socket and fcu next to it.

because it's probably joined into an inaccessible Jb under the oak floor. i'd just bung in an unswitched FCU with a 3A (or 5A) fuse before the light switch.
 
Replace the 1.5 feeding the switch (replace switch with FCU) with 2.5 simples it aint rocket science it's in the OSG plain as the nose on your face, no arguments just do it right the first time as Mike Holmes says.
 
Put it this way, if I carried out a job whereby I fed a FCU with 1.5mm from a ring final and some muppet came arond telling the customer it's bad practice and against regulation blah blah blah... That is SLANDER! Plain and simple! If you then proceeded to charge the customer to replace it that is obtaining money by deception, a criminal offence!

Any of you idiots out there that continue to propagate this myth that somehow the 1.5mm cable isn't protected are talking out of your rear end. I would suggest that you start by picking up a bloody regs book!!!
 
Replace the 1.5 feeding the switch (replace switch with FCU) with 2.5 simples it aint rocket science it's in the OSG plain as the nose on your face, no arguments just do it right the first time as Mike Holmes says.

Why?

Yes look at the guide for a guide (sarcasm), while at the same time ignoring the forward fusing rules (section 434) in the BGB.

Even the picture in App 15 tells us it does not cover other aspects of the design.
 
If I was installing this from scratch I would fuse down at the point of CCC reduction. If it was already present and as described by the OP, I would leave it as it is, there is absolutely nothing wrong with it.
 
I would suggest that you start by picking up a bloody regs book!!!

OK, to continue the discussion I'll try ....... as I understand the regs the C/B is installed to protect the cable, which in this case I read it as a 32A C/B protecting the 1.5mm cable fed off 2.5mm cable. So the 1.5mm cable isn’t being overload protected by the 32A C/B.

But regs do allow that if due to the cable load characteristics it isn’t likely to be overloaded then overload protection isn’t needed --- provided there is fault protection. For the 12V lights connected via a transformer I’ll take this as holding true for overload and the 1.5mm cable is good to use without circuit overload protection.

However, Ive still got to provide fault protection for this 1.5mm cable even though I don’t need overload protection. I’ll assume an RCD so a L/E fault is taken care of but what about a L/N fault? Will the cable hold out before the 32A C/B or DNO cut-out “pops”?. Using the let thro current calc will probably show the 1.5mm cable can handle this energy and is OK to use.

But if it cant handle the fault, how do I now provide fault protection for the 1.5mm cable?
 
Last edited by a moderator:
OK, to continue the discussion I'll try ....... as I understand the regs the C/B is installed to protect the cable, which in this case I read it as a 32A C/B protecting the 1.5mm cable fed off 2.5mm cable. So the 1.5mm cable isn’t being overload protected by the 32A C/B.

But regs do allow that if due to the cable load characteristics it isn’t likely to be overloaded then overload protection isn’t needed --- provided there is fault protection. For the 12V lights connected via a transformer I’ll take this as holding true for overload and the 1.5mm cable is good to use without circuit overload protection.

However, Ive still got to provide fault protection for this 1.5mm cable even though I don’t need overload protection. I’ll assume an RCD so a L/E fault is taken care of but what about a L/N fault? Will the cable hold out before the 32A C/B or DNO cut-out “pops”?. Using the let thro current calc will probably show the 1.5mm cable can handle this energy and is OK to use.

But if it cant handle the fault, how do I now provide fault protection for the 1.5mm cable?

Going round in circles here, see my earlier post. Fault protection will be supplied via the CB.
 
Fault protection will be supplied via the CB.
True, if the 32A C/B can do the trick for 1.5mm cable?!?!. But the question was aimed that if the 32A C/B cant (and there isnt an FCU fitted for overload protection) how is fault protection now covered?
 
True, if the 32A C/B can do the trick for 1.5mm cable?!?!. But the question was aimed that if the 32A C/B cant (and there isnt an FCU fitted for overload protection) how is fault protection now covered?
I understood from OP that there is FCU fitted, this give overload protection.

From reg 434.5.2 the 1.5mm cable will reach its limiting temp in about 1.6 seconds (assuming 160A fault current) As the CB will operate in about 0.1 seconds, at this current, fault protection is afforded
 
I understood from OP that there is FCU fitted, this give overload protection.

Sorry if my reply has confused but the thread is directed along there being no FCU fitted for protection, hence my question for how to protect for fault current in the unlikely event that the 32A C/B cant!.
 
you are right that you can take lighting off a ring final circuit and I know its bad practice to use 1.5mm cable to do the first leg of that circuit extension with but as 1.5mm can carry up to 16A, that first leg will only be carrying the load of the lighting to which you will have a 5A fuse in series. so I would make sure firstly that the 1.5mm does not form part of the ring final circuit and if this proves so then I would have said it is ok to remain. just note as a code 3 on your report.
 
youre all missing the point !
the OP declared this to be an eicr , therefore the only discussion should about the coding if any.
and IMO its probably a C2 - but a 2 minute fix with a switched fused spur.
 
but even after prominant members in here made it quite clear that it was acceptable to use a 1.5 as a feeder to an FCU there were still several others continuing blubbing on about how they would rip out the 1.5 and replace with 2.5....
an unneccessary nonsense if you ask me
christ, what do some in here think we fuse down for?
 
Last edited:
but even after prominant members in here made it quite clear that it was acceptable to use a 1.5 as a feeder to an FCU there were still several others continuing blubbing on about how they would rip out the 1.5 and replace with 2.5....
an unneccessary nonsense if you ask me
christ, what do some n here think we fuse down for?

The fun of it?

Lecky takes easiest route so splicing cable then adding fcu would be more than adequate.

If i was installing myself though id probably use 2.5 to fcu but woudlnt replace if it was done in 1.5
 
but even after prominant members in here made it quite clear that it was acceptable to use a 1.5 as a feeder to an FCU there were still several others continuing blubbing on about how they would rip out the 1.5 and replace with 2.5....
an unneccessary nonsense if you ask me
christ, what do some n here think we fuse down for?

prominent, glenn. get a grip, man. :angelsad2:
 
What really scares me with threads like this is how many so called electricians seem to think it is dangerous to utilise the 1.5mm to a fused spur, as stated by Glenn spark and others it is perfectly ok to do this, I sometimes wonder where the train of thought comes from to rip someone's house apart just because they don't seem to understand the basics of electrical work.
 
What really scares me with threads like this is how many so called electricians seem to think it is dangerous to utilise the 1.5mm to a fused spur, as stated by Glenn spark and others it is perfectly ok to do this, I sometimes wonder where the train of thought comes from to rip someone's house apart just because they don't seem to understand the basics of electrical work.
its a waste of time as well when after stating such facts there are still those that refuse to listen..
and so will go forth and ruin decor/cost unneccessary cash/invent non-existant remedial works....all a con..as Damian quite rightly pointed out earlier in this nonsense...
 
its a waste of time as well when after stating such facts there are still those that refuse to listen..
and so will go forth and ruin decor/cost unneccessary cash/invent non-existant remedial works....all a con..as Damian quite rightly pointed out earlier in this nonsense...

It really is crazy mate and the scariest part is like you said they can't understand it which in my view means they shouldn't be in the game.
 
It really is crazy mate and the scariest part is like you said they can't understand it which in my view means they shouldn't be in the game.

So electricians that taught me this trade,don't know what their talking about!! (1979) some are proberly not with us any more, and proberly before you was born!!. Close this ****in thread!!
 
Last edited:
It really is crazy mate and the scariest part is like you said they can't understand it which in my view means they shouldn't be in the game.

I disagree it fills me with a sense of joy to hear people say such stupid stuff cause it means that they will always be creatin work for others that will be far less cheaper cause they haven't quoted to tear the house apart for no reason! Good electricians won't ever have to worry about any recessions!
 
So electricians that taught me this trade,don't know what their talking about!! (1979) some are proberly not with us any more, and proberly before you was born!!. Close this ****in thread!!

Why ?,

don't you understand it ?

We could have had crap electricians in 1979 who didn't understand it then either lol.
 
Why ?,

don't you understand it ?

We could have had crap electricians in 1979 who didn't understand it then either lol.
Although, wouldn't have had forums then, or computers, or people banging on about Part P, or people banging on about Electrical Trainee, or Aids, or the Olympics in London, or robots. But wine was cheaper :)
 
So electricians that taught me this trade,don't know what their talking about!! (1979) some are proberly not with us any more, and proberly before you was born!!. Close this ****in thread!!
It doesn't matter who was born when or who taught who, the point is that if you think that you need to rip out a 1.5mm cable to protect it from some magical fault between fcu and the ring then we've all got bigger problems than I thought oh and don't forget to pick your dummy up :53:
 

Reply to Lighting circuit taken off ring main somewhere in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
790
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
810
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock