- Reaction score
- 1
Hello everyone
I'm picking up some remedial works from an EICR fail in a commercial property.
Its a 3 phase supply with old steel conduits , trunking & coupled metal equipment, that provides the earth to the various locations.
At present the earthing is insufficient, every earth in the building comes via the continuous metal structure of the installation.
The supply looks very old, the incomer is wrapped in a cloth like material & it looks to be a TN-S system, the earth looks to be the armour of the cable, connected into a chalk block terminal, then there is a old & uninsulated 10mm cable connected to the main earth boss on the metal trunking, from there the 3 main isolators are coupled to the trunking & feed various areas & DBs, each isolator has a exterior earth connection & at present they are all linked together with uninsulated 6mm2 cable!
The values back to earth are pretty good from even the furthest off DB, 0.21 ohms.
I was planning to upgrade the main earth link, from the main earth to the trunking to 16mm2 & renew the external earthing of the metal enclosures to 6mm2.
Is this correct?
Thanks
I'm picking up some remedial works from an EICR fail in a commercial property.
Its a 3 phase supply with old steel conduits , trunking & coupled metal equipment, that provides the earth to the various locations.
At present the earthing is insufficient, every earth in the building comes via the continuous metal structure of the installation.
The supply looks very old, the incomer is wrapped in a cloth like material & it looks to be a TN-S system, the earth looks to be the armour of the cable, connected into a chalk block terminal, then there is a old & uninsulated 10mm cable connected to the main earth boss on the metal trunking, from there the 3 main isolators are coupled to the trunking & feed various areas & DBs, each isolator has a exterior earth connection & at present they are all linked together with uninsulated 6mm2 cable!
The values back to earth are pretty good from even the furthest off DB, 0.21 ohms.
I was planning to upgrade the main earth link, from the main earth to the trunking to 16mm2 & renew the external earthing of the metal enclosures to 6mm2.
Is this correct?
Thanks