Discuss MBPC to steel columns in warehouse area in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
649
Steel columns for building into concrete… no inter- connection of Beams … Wooden beams used for interlinked supports … would MBPC be required to each column…
 
Interesting situation, as each of those columns in to a concrete base would defiantly count as an extraneous conductive part. My view is though ought to be bonded as I guess they are all within some sort of distance that contact with the installation's CPC system is possible.

They would not all need to go back to the MET but probably you could zig-zag some bonding from MET to one column and then across wood beam tops or similar to link them all up in some pattern with (hopefully) sane length of bond wire.

Is it TN-C-S ?
And is it needing more than 10mm bond?
 
Interesting situation, as each of those columns in to a concrete base would defiantly count as an extraneous conductive part. My view is though ought to be bonded as I guess they are all within some sort of distance that contact with the installation's CPC system is possible.

They would not all need to go back to the MET but probably you could zig-zag some bonding from MET to one column and then across wood beam tops or similar to link them all up in some pattern with (hopefully) sane length of bond wire.

Is it TN-C-S ?
And is it needing more than 10mm bond?
Yea …. It’s an existing building dating back some years … never got a mention before..came up on EICR… linking these columns approx 300m 10mm Earth cabling… quite a job… will test to see if they are extraneous
 
You might also want to check if they are linked by steel/rebar foundation works (i.e. resistance column-column below 0.1 ohm or so) in which case bonding one (or two, depending on how many are electrically linked in groups) would do.
 

Reply to MBPC to steel columns in warehouse area in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Visual on installation when replacing a couple of faulty fittings. No continuity on steel structure of building, EICR not available @ time of...
Replies
7
Views
839
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
535
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Replies
3
Views
627
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
853
So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel...
Replies
5
Views
911

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock