Currently reading:
PME system with earth rod aswell

Discuss PME system with earth rod aswell in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Too many mirrors David.

This reminds me of a house I moved in to in 1975 built in 1936. After a few years I decided to check the earth out as I noticed we had 2 overhead wires + and -. There was no earth system at all so I
Bought an earth rod and wired it to the fuse box accordingly.
Then the MEB came and wired the earth to neutral WTF. If that had never been brought in would they allow that now?
I think they also used to use a 12" square galvanized plate buried in the ground. I've just dug one up here, house built in 1934.
 
and this week's prize for the most duplicate posts goes to..................................................................................................................................................................................................

the rabbit.
 
Let’s open an old thread.

looking fo4 a brief answer. Wishful thinking.

on a pme system having an earth rod as an addition is perfectly ok in my opinion.


im working for and under a new electrician at work.
we have had a distribution board fitted by outside contractors. They have earthed via a 16 mm earth conductor within the 3 phase SWA supplied from a PME system. They have also popped an earth rod in at the new distribution board. We are going to run feeds of this board for various stuff.

the new electrician wants to convert to TT or get rid of the earth rod As he thinks it’s wrong because of “potential differences” I disagree.

Am I wrong? I’m willing to accept this If I am,

but I know earth rods where proposed as additions in PME in the 18th. So I’m sure it’s OK.
 
Let’s open an old thread.

looking fo4 a brief answer. Wishful thinking.

on a pme system having an earth rod as an addition is perfectly ok in my opinion.


im working for and under a new electrician at work.
we have had a distribution board fitted by outside contractors. They have earthed via a 16 mm earth conductor within the 3 phase SWA supplied from a PME system. They have also popped an earth rod in at the new distribution board. We are going to run feeds of this board for various stuff.

the new electrician wants to convert to TT or get rid of the earth rod As he thinks it’s wrong because of “potential differences” I disagree.

Am I wrong? I’m willing to accept this If I am,

but I know earth rods where proposed as additions in PME in the 18th. So I’m sure it’s OK.

If the rod is bonded to the distribution board earth then surely there can be no potential difference. Did he mention which two points he was thinking of the difference being across?

I agree with you and really can't see the problem here, but it will be interesting to hear other views.
 
If the rod is bonded to the distribution board earth then surely there can be no potential difference. Did he mention which two points he was thinking of the difference being across?

I agree with you and really can't see the problem here, but it will be interesting to hear other views.
Thanks for quick responce. My thoughts exactly. Just had to check in case I had got it wrong.


This new guy has much more experience with these types of systems than me or so he said at interview, coming from industrial and comercail instals, but I’m starting to suspect he’s been relying on others to design his jobs.
 
Thanks for quick responce. My thoughts exactly. Just had to check in case I had got it wrong.


This new guy has much more experience with these types of systems than me or so he said at interview, coming from industrial and comercail instals, but I’m starting to suspect he’s been relying on others to design his jobs.

To be honest I'm no expert either.

Be interesting seeing what else he says.
 
How certain are you it is a PME system, TN-C-S is not necessarily PME.
It’s a very large installation with its own substation clearly labelled PME. Also the installers who fitted the Distribution board have noted it as PME.

I am going to have a chat with the installers as we have a good working relationship with them.

I just wanted to run it past you guys first in case I made a fool of myself.
 
Let’s open an old thread.

looking fo4 a brief answer. Wishful thinking.

on a pme system having an earth rod as an addition is perfectly ok in my opinion.


im working for and under a new electrician at work.
we have had a distribution board fitted by outside contractors. They have earthed via a 16 mm earth conductor within the 3 phase SWA supplied from a PME system. They have also popped an earth rod in at the new distribution board. We are going to run feeds of this board for various stuff.

the new electrician wants to convert to TT or get rid of the earth rod As he thinks it’s wrong because of “potential differences” I disagree.

Am I wrong? I’m willing to accept this If I am,

but I know earth rods where proposed as additions in PME in the 18th. So I’m sure it’s OK.
An Earth electrode/pit in a TN-C-S installation should be encouraged! In fact many (most?) countries mandate it! A large installation may need a fairly low impedance to be effective though.

But as pointed out TN-C-S could be either PME or PNB.
 
Last edited:
An Earth electrode/pit in a TN-C-S installation should be encouraged!
I would agree with you on a properly maintained, regularly checked system but one or multiple earth rod issues could become dangerous as I have seen in the past
In fact many (most?) countries mandate it!
And they all have different regs and network topology
A large installation may need a fairly low impedance to be effective though.
And that is the difference between an earth rod and a properly installed and tested earth rod
But as pointed out TN-C-S could be either PME or PNB.
With a private substation it could be TNS despite it being labelled PME just because the star point of the transformer is referenced to earth it is only there to keep a stable neutral point and doesn't necessarily make it PME
 
I know all the over head cables locally have been switched to PME. However that does not necessarily mean that my installations supply is.

I think most supplies these days have an element of PME as all repairs additions and alterations in the network are going to PME.

having a part of the supply that has been replaced to PME . Does that nessisaritly mean the installation is classed as PME. If it was formally TNS?

I’ve been watching some John ward you tube videos and it has raised more questions than answers.



Anyway forgetting about the merits of PME with or without an earth rod.…

Ive decided the following. I think we should TT it.
the supply we are going to take off the DB in question is going to 3 separate metal containers with an outside enclosure for keeping birds (Parrots). Each container will have a separate small DB for the final circuits.
The nature of the metal containers and its for livestock has convinced me that TT is the better option especially considering the difficulty in identifying earthing arrangements despite labelling. There won’t be any suplimentary bonding issue as there is no other utility supplies. No water or gas contained within.
obviously earthing to the equipot3ntial metal enclosure will happen as it’s in contact with the mass of earth.
Any buried water pipes in the vicinity we know are plastic as we put them in so no issue there.
 
It’s a very large installation with its own substation clearly labelled PME. Also the installers who fitted the Distribution board have noted it as PME.

If it has its own dedicated feed from a substation then it can't be PME. For a supply to be PME there needs to be multiple N-E connections along a distributing main, it's not possible to achieve that multi earthing on a dedicated feed.
 
If it has its own dedicated feed from a substation then it can't be PME. For a supply to be PME there needs to be multiple N-E connections along a distributing main, it's not possible to achieve that multi earthing on a dedicated feed.
Surely you can if you have multiple earth rods connected to the PEN conductor before the main isolator (origin of supply)??
 
I don't think so, I'd have to look up the rules and regulations around PME to be sure though.
It just wouldn't make sense for a dedicated feed from a substation.
To be fair, I am not certain myself
but I thought it Simpley meant that the N was referenced to earth at several points before the origin. This becoming a combined N and E when terminated at the origin.
 
Draw him a diagram showing how the PME earth will have a mini electrode somewhere.
It’s nuts to get rid of a TN system for this reason. As you say it’s even in the regs book now.

If the phases are very unbalanced and the closest PME real earth point isn’t near or has high impedance then there could be a measurable potential difference but it would have to be large to take this action - id prefer to be talking to the DNO about it.

(There’s a formula in the EV section to calculate N current in an unbalanced 3 phase system btw)

Edit - I missed some later posts, sorry
 

Reply to PME system with earth rod aswell in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock