Currently reading:
Proving structural steel is bonded

Discuss Proving structural steel is bonded in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
52
Carrying out some EICR on a commercial/industrial site.
Previous records state the structural steel is bonded, and visually I can see 4x 25mm Earth wires leaving the main earth bar, I cannot trace the one going to the steel , though I suspect one of these does.
How do I prove this? Is it a case of isolating all power( an operational minefield) and testing between the steel and out going 25mm earth wires?

On a second point if I may, neutrals not in order on a large 3 phase DB so I disconnected neutral link bar and tested NxE at outlet end (500v) and still got a reading at less than one ohm.
The cables are in good condition , and the breaker dosent trip when in use , so I do not think it is a dead short.
Any body any pointers on these? It may be I'm missing something simple, my head is bursting today! And any help/ is greatly appreciated .
Thanks in advance
 
Carrying out some EICR on a commercial/industrial site.
Previous records state the structural steel is bonded, and visually I can see 4x 25mm Earth wires leaving the main earth bar, I cannot trace the one going to the steel , though I suspect one of these does.
How do I prove this? Is it a case of isolating all power( an operational minefield) and testing between the steel and out going 25mm earth wires?

On a second point if I may, neutrals not in order on a large 3 phase DB so I disconnected neutral link bar and tested NxE at outlet end (500v) and still got a reading at less than one ohm.
The cables are in good condition , and the breaker dosent trip when in use , so I do not think it is a dead short.
Any body any pointers on these? It may be I'm missing something simple, my head is bursting today! And any help/ is greatly appreciated .
Thanks in advance
Are you oingthis EICR as part of your apprenticeship, or on the QT for some extra dosh?
 
For the bonding just use a wander lead and test back to the MET.

As for the N-E fault, the MCB won't trip but an RCD would.

Are you competent to carry out periodic inspections?
 
wandering lead method and sometimes visual verification
(once during a christmas shutdown some copper scrounging git clipped all the bonding conductors from all the i beams) we found them missing on startup inspection and they were replaced.
 

Reply to Proving structural steel is bonded in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock