Currently reading:
New Zealand rcbo leakage tripping

Discuss rcbo leakage tripping in the UK Electrical Forum area at ElectriciansForums.net

S

singingfraggle

Hi guys I have a client whos rcbo keeps tripping, never when I am there and at all times day and night.i have stripped circuit down insulation readings all over 200meg ramp test on rcbo is 21ma . should this be higher or is it ok thanks paul
 
ramp it first with all loads disconnected..(you`v done this already)...
then ramp it again with all loads connected....
the difference is leakage....
I would be changing that RCBO n all....
but confirm the leakage present first wont you...
i`v told you how to do it...
 
I had this situation with one of my clients on a rewire I did.
there is 2 options (which worked for me)
1. offer to PAT Test all appliances within the property
2. Tell them to keep a record of what is plugged in (turned on or off) when the RCBO tripped - or tell them just to call you as soon as it trips and not to touch anything - not even turn it back on!
 
A wander lead is a handy piece of kit and so is a nice long extension lead.
These 'trips' are trial and error and testing will show zilch a lot of the times.

As the guys have already said..............there are always 'prime suspects' so......................

Plug your nice long extension cable into another cct ( upstairs ring?) then plug in the prime suspect ( freezer?) and see if the rcbo still trips..............etc etc until you find the culprit:)
 

Reply to rcbo leakage tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock