Search for tools and product advice,

Discuss RCD testing issues in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
Hi all,

Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into account, I have not done any testing for the last 3 years so please be gentle with the below.i feel very rusty.

My neighbour has asked for my help with RCD nuisance tripping. His little brother has temporarily moved into his spare room and brought with him some computer gear. Since then the main RCD has tripped a few times (once in the middle of the night). Finger is firmly pointed at this being the issue.

I have done an earth leakage test on the board. No circuit is causing any more than 2mA of leakage (with all the PC gear turned on).

I tried to test the 30mA AC up front RCD directly with all circuits isolated but it would not trip, it would however trip if I tested from one of the circuits (when energised). My first head scratcher. The trip time was 15mA at x1.

I did attempt to move the upstairs sockets onto the non RCD side of the board as a temporary measure to see if the problem persisted however, as soon as I moved the neutrals to the non RCD neutral bar, it tripped the rcd. My second head scratcher.

I have ran out of time because I needed to take the kids swimming but my thoughts are, the RCD is faulty considering the 15mA trip current. The upstairs RFC which I attempted to move to the non RCD side must be connected to the RCD somehow via a shared neutral or similar.

Would be good to hear your thoughts.

The board is an Volex. RCD is a volex VR63.
 
You need to test the upstairs circuit and check any interconnections to neutral of the RCD side.
I wouldn't recommend removing it from the RCD even as a temporary measure.

Yeh I agree. I did do end to end test on the neutral RFC which came back as 0.95 ohms.

I will have to look at the circuit in more detail
 
I tried to test the 30mA AC up front RCD directly with all circuits isolated but it would not trip, it would however trip if I tested from one of the circuits (when energised).
I'm suggesting this because it's a mistake I made once, when I wasn't thinking clearly: Did you test the correct side of the RCD?

I would be carrying out insulation resistance tests first, to rule out any faults in the circuits or equipment. Test L+N to E at 250V, with everything left plugged in/switched on.
 
I'm suggesting this because it's a mistake I made once, when I wasn't thinking clearly: Did you test the correct side of the RCD?

I would be carrying out insulation resistance tests first, to rule out any faults in the circuits or equipment. Test L+N to E at 250V, with everything left plugged in/switched on.
Doh. What a dumbo.
 
Assumption is the mother of all major foul-ups!

Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as circuits are powered on.

An RCD that fails to trip-test on its own is deeply suspicious, but until you have ruled out N-E faults an anything still connected (i.e. it is not really "on its own") there is no point in jumping to that conclusion.
 

Reply to RCD testing issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
386
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
482
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock