Search for tools and product advice,

Discuss Ring spotlight on old house help in the DIY Electrical Advice area at ElectriciansForums.net

Magw1tch

DIY
Reaction score
0
Hi all, I’ve purchased a Ring Spotlight camera and decided to remove the old spotlight that’s currently installed on the house we recently purchased. After taking down the old spotlight, I found four wires: black, brown, unsheathed earth, and grey. However, the Ring only has the usual three wires: live, earth, and neutral. Any ideas on how to wire up the Ring? Any advice would be greatly appreciated. Ohh and i cant find a switch for this as someone stated that it may be connected to a switch somewhere
 
We’re all the cores connected before, or was one unused?

It used to be that you took a live, a switched live and a neutral (ignoring the earth, as it’s the obvious one)
The live powered the sensor part of a light with PIR, and the switched live was connected on the line between the sensor and the light part as an over ride function.

Nowadays, the sensors are overridden by turning the switch on-off-on quickly… only needs the L and N.

Standard, the brown is usually the permanent live, the black is the switches live(should be identified … normally with brown sleeving or tape) and the grey is neutral.

I say usually, but there was and still is a times when the black is neutral and the grey is switched live… It just depends who did the work in the first place.


The earth should also be sleeved in green and yellow…


There must be a switch for it somewhere… is there a switched fuse plate next to a socket perhaps?
It’s not necessarily supplied from a lighting circuit.


A quick word on safety. Isolate at the consumer unit… especially if you can’t turn it off
 
I did take this picture before of the wiring in the spotlight if that helps. The earth is bottom right I cut this to get the sleeve off to put onto the new wire
 

Attachments

  • IMG_4033.jpeg
    689.1 KB · Views: 9

Reply to Ring spotlight on old house help in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, thanks in advance for any guidance you can provide. I will of course turn off everyhing at the consumer unit before doing anything. I...
Replies
0
Views
468
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
594
Good evening. My son in law has moved into a 5 year old house with a conservatory. There is a 3 core and earth lighting cable poked through from...
Replies
8
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
589

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock