Search the forum,

Discuss Steel Awning frame outside EP zone, bondit? in the UK Electrical Forum area at ElectriciansForums.net

John-

-
Reaction score
48
Hi

customer had installed a 10m awning that is secured to a very substantial 6” box steel frame, concreted in either end - large goal post if you will. It is fitted on the garden patio, just outside the entrence to his living area accesd by sliding doors. The motor is a low current single phase motor that moves the awning in and out quite slowly. There is no fortuitous or deliberate connection to earth between the motor CPC and the aluminium awning box. A 3 core flex is run on top of the steel work into and RCD socket. I am looking at upgrading the MCB to RCBO. I have no details yet from the manufacturer - i will look to getting these. It is a TNCS supply.

Question is, should i bond the steel work to the motor CPC at lesst? Technically it could be classed as structural. If so it would need a much bigger conductor... Or do i just leave it alone? My call is that this is extranious and should be bonded to the supply of the motor. It is on the threshold between EP zone and simultaneously accessible for both. He wont go for 10mm cable back to dis board, pretty sure he will go ape with a bit of 4mm on show... ?
 
Have you tested to confirm that it is an extraneous conductive part? You might find it’s not and doesn’t need bonding at all.

Can you touch both the frame and something that might be at a different potential at the same time? Say the awning frame and a nearby, bonded, supply for an outside tap?
 
Its 12k today, it’s not an Extranious part today i guess. No other touch points today but there could be. The aluminium housing of the awning is secured directly to the steel. That’s my biggest worry.
 
Not knowing the layout or positioning of the awning has anyone considered if lightning protection might be needed with all this metalwork
 
This may be of some help
 

Attachments

  • A3D479FB-B970-4013-BE30-C98ABA0FF790.png
    654.6 KB · Views: 37
Could bonding it present a risk which was not otherwise there due to it being a TN-C-S supply

Risk of metal frame voltage rise difference to the ground around it from a PEN conductor fault, or even tingles from normal PEN conductor volt drop
 

Reply to Steel Awning frame outside EP zone, bondit? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock