- Reaction score
- 1,650
A client has recently had a 10ft x 6ft Steel Cabin delivered. It will be a permanent addition for a block of flats outside for storing things in for contractors. They want a light inside and a floodlight outside.
Currently next to it about 5 yards away is a bin store which has a light in it from the main building which is on a 6A supply. The earthing System is PME. I can’t run a dedicated supply from the main building due to the amount of paths and obstacles now in the way.
Not keen to continue the PME into the steel container as it’s permanent, I’d rather TT. I have thought about coming from the Bin store supply into a 3A FCU, TTing the outgoing supply here and going into the cabin with this. Any thoughts?
Currently next to it about 5 yards away is a bin store which has a light in it from the main building which is on a 6A supply. The earthing System is PME. I can’t run a dedicated supply from the main building due to the amount of paths and obstacles now in the way.
Not keen to continue the PME into the steel container as it’s permanent, I’d rather TT. I have thought about coming from the Bin store supply into a 3A FCU, TTing the outgoing supply here and going into the cabin with this. Any thoughts?