I need to install a charger for an electric car, which needs 60 amp breaker. My main panel has a 200amp breaker and services 2 sub panels, both via 60 amp breakers. My issue is that there is no space in the main panel for a 60A 240V breaker. I do have space in one sub panel (basement) which is ideally situated to service the charger in the garage. The cable to this sub panel is ‘AL type se style r type xhhw 600 3 cdrs 2 awg’. Would I be able to change the breaker serving this sub panel from 60 to 90 amps in the main panel, then add a 60A breaker in the subpanel for the charger?
 
I need to install a charger for an electric car, which needs 60 amp breaker. My main panel has a 200amp breaker and services 2 sub panels, both via 60 amp breakers. My issue is that there is no space in the main panel for a 60A 240V breaker. I do have space in one sub panel (basement) which is ideally situated to service the charger in the garage. The cable to this sub panel is ‘AL type se style r type xhhw 600 3 cdrs 2 awg’. Would I be able to change the breaker serving this sub panel from 60 to 90 amps in the main panel, then add a 60A breaker in the subpanel for the charger?
Pictures would be nice but do not change that breaker to a 90 amp. You can buy slim line breakers and free up space. Just because you have to install a 60 amp service, don’t mean that it’s going to pull 60 amps. At best it will pull maybe 25- 35 amps maximum
 

Reply to Sub panel breaker amperage upgrade in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
931
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
754
Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
966
New member and DIY. I have a 60 AMP breaker going to a sub panel for a workshop. Two months ago I bought an electric car and a 40 AMP charger...
Replies
7
Views
1K
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
967

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock