Discuss Surge on community center with flat in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
60
Hi all, got a community center job and the want surge protection, 3ohase in phase for community center and phase for the flat upstairs, question is, do fit surge at the incomming covering both installs or fotfor community center and inenfornflne for the flat ?
 
usually a surge device is best fitted next to the distribution board it is protecting, if you have 2 different boards fit 2 units, unless of course the main board is supplying the smaller one and then one device would be adequate, however a picture posted up on here may suggest a better way is the way forward, admittedly this was 9 months ago and an old thread but if the OP is still around it would be interesting to see what was actually done.
 

Reply to Surge on community center with flat in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Article
If you search the internet for PCB manufacturing, you will find many companies, houses, and fabs that offer cheap PCB manufacturing and...
Replies
1
Views
781
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC...
Replies
7
Views
408
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
525
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
316
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock