Search the forum,

Discuss Surge protection for solar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
13
Hi, We're looking at installing solar at a remote property which is on a TT system with out buildings supplied with underground cables (Stables, tractor sheds...) The array will be installed on one of these out buildings and I am trying to navigate 443.4.1 to assess if it requires an SPD on the DC cables. Quick side note, for the cost, we would have probably installed it either way, but I have an inquisitive mind that needs to understand rules and regs. Anyway, in my opinion, neither the stables nor tractor shed fall under any of the 3 idents of 443.4.1.

I would like to see others opinions on whether an SPD is 'technically' required please.

It would be useful if there were refresher courses as and when the regs change for different electrical services (PV, EV, EESS....). It feels a bit steep to charge for the full course again and get the same certification twice in an attempt to try and gain an understanding of these changes, I did my PV course a few years ago and looking at the code of practice, a lot has changed since then.
 
Those 3 indents are where SPDs shall be provided no matter what.

However the regulation goes on to say that SPDs shall be provided for all other cases, unless the owner says they don't want them and they accept the risks involved.

In my view, this refusal should be accompanied by a signed statement to that effect.

The only question would be whether the proposed new work would warrant adding SPDs, if for example, the new work was just adding an extra socket to an existing circuit. There doesn't appear to be any clear guidance regarding this aspect.
 

Reply to Surge protection for solar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock