Discuss Twin and Earth American style in the USA Electrical Forum area at ElectriciansForums.net

Reaction score
95
Can anyone tell me more about Twin and Earth American style?

SUPPU.jpg

What's it's full name? NM?
Is it always flat?
Do you add a sheath to the ground/earth cable?
Thanks 😊
 
Only fact I've learned about the stuff is it's commonly known by the brand name 'Romex'.

Google tells me NM stands for non-metallic (sheathed).

Edit: Earth generally left bare according to this fairly informative page.
 
Pretty much all YOuTube sparks in America and Canada refer to that cable as ROMEX , which I believe is a brand name. It is much harder than pvc twin and earth , it is much more like our LSF cable. Yes the NM stands for Non Metalic.
It comes in a wide variety of gauges much like our twin and earth does where the line and neutral come sheathed and with a bare copper earth / cpc / ground wire.
Yes it is always flat with The main difference being they have a White for Neutral and Black/Very dark grey for Live.
Also from what I can tell you are not allowed to wire Romex surface mounted , it must either be in the fabric of the building Or run in a conduit.
This guy waffles a fair bit and even muddles up his colours but he explains the different sizes , and colours of Romex common in his area

 
Last edited:
American / Canadian terminology for everything is so bizarre, not to mention they can mix lighting and receptacles ( sockets ) on the same circuit and can have receptacles ( sockets ) in bathrooms

also the fact the the bigger the gauge on the wire the smaller it actually is , this had be stumped for ages when watching American YouTube stuff.
 
Yes once you actually understand the smaller the gauge the larger the wire it makes sense , but for anyone watching an American vid it must be a head scratcher at first

As the gauge only goes up to 0 , I believe they also have 00 and 000 gauge wire in America because the original SWG doesn't go big enough
 
they can mix lighting and receptacles ( sockets ) on the same circuit

This is normal nearly everywhere except UK. Our need to strictly separate lighting and sockets comes mainly from our use of 32A circuits which in turn comes from fused plugs. We used to be able to put lights and 5A sockets on the same circuit (and still do, for controlled lighting sockets) but 32A (or 30A as it was originally) is too big to mix with lighting.

for anyone watching an American vid it must be a head scratcher at first

We used to use gauge numbers for British wiring cables too, obviously SWG rather than AWG, before we went to the strand diameter in inches. So the cable we remember as 3/.029 started life as 3/22 - likewise it's not a fraction but the number of strands and the SWG separated by an oblique. I have a number of early British electrical books that reference cables sizes in this way. Many of the fractional inch sizes are equivalent to SWG: .036" = 20SWG, .064" = 16SWG. Some aren't, 0.044 wasn't an SWG size IIRC. Although the principles of AWG and SWG sizing are the same, the actual dimensions differ.

Main differences of USA NM from UK T+E:

  • Ground conductor is same size as others
  • Core insulation is 2-layer, PVC has a skin
  • NM-B is 90 degree rated, and is now standard
  • Sheath of newer cables is colour coded to identify size
  • Size quoted in the form 12-2 where 12 is the AWG and 2 the number of cores other than ground
  • Colours W & B / W, B & R
 
Was UK T+E ever in imperial sizes? If so what was for example 2.5mm
That is one for the OGs on here to tell you about , but in a nut shell yes pre modern T&E there was a stranded flat cable with pvc sheath and before that a rubber sheath that came in various gauges
 
Was UK T+E ever in imperial sizes? If so what was for example 2.5mm

Indeed, it was imperial for longer than it has been metric. Until 1966 not all flat cables had an earth core, they were called flat twin, flat triple, flat twin & earth etc. The same sizes were usually available in lead-sheathed or rubber-sheathed as desired, up to the introduction of PE and PVC insulated. The conductors of imperial-sized cables are usually tinned copper rather than plain.

First, as I mentioned above, it was in SWG sizes. The conductors were quoted as the number of strands and their SWG, for example 7/22 (which is not a fraction) meant seven strands of 22 SWG.
Then we switched to identifying the strand size by diameter in inches, so 7/22 became 7/.029 (note position of dot and zero)
That was the nearest to 2.5 sqmm, actually nearer 2.9
Normal lighting circuits were wired either in 1/.044 which is like 1.0 sqmm, or the larger and more flexible three-strand 3/.029.
Next up was 3/.036 and 7/.029 for sockets. 7/.044 was about the largest regularly used as flat twin or twin & earth, above which it tended to be singles in conduit.

The odd one out was imperial MI, for which the conductors were always sized in sq. ins. instead off ins. diameter, although the cable sheath was sized as ins dia.
 
Last edited:
Going off-topic again I was doing a job lately and there was some silk? covered cables in very old conduit. The conduit was in great condition it was black. Could still use it really and the cable wasn't in bad condition really. Don't worry it wasn't actually in use. Just under the boards.

I wanted to post a pick on here but think someone chucked it.
 
Unlikely to be silk, which was only used for very fine coil winding wires due to cost. Before PVC, the normal insulation for British conduit cables was VIR, vulcanised rubber covered with an impregnated cotton braid. The rubber provided the insulation, the cotton provided the strength and abrasion resistance, and the impregnation protected it against rot. Other woven coverings for power cables included polybutyl jute and cambric.
 
That's ordinary VIR conduit cable, I can't see the conductor to say what size it is. Rubber extruded over the conductor (sometimes in two layers) and the braided cotton serving over the top. There's thousands of miles of this stuff still in use, decreasing rapidly now but not all gone yet. The same is true of the nearest USA equivalent. They used a version with a heavier cotton braid but basically the same concept.

When the rubber-insulated cores were used inside a rubber or lead sheath, instead of the woven cotton braid they were usually lapped in cotton tape.
 
Can anyone tell me more about Twin and Earth American style?

View attachment 107858
What's it's full name? NM?
Is it always flat?
Do you add a sheath to the ground/earth cable?
Thanks 😊
NM or Romex is flat for 14/2, 12/2, or 10/2 or 3 conductor. Starting at # 8 or # 6 is normally round. I still can’t understand why we have naked grounds but it’s easy to purchase shrink tubing that can be installed on the naked wire. Be sure and mark it green.
 
Thanks for the info.
NM or Romex is flat for 14/2, 12/2, or 10/2 or 3 conductor. Starting at # 8 or # 6 is normally round. I still can’t understand why we have naked grounds but it’s easy to purchase shrink tubing that can be installed on the naked wire. Be sure and mark it green.
Thanks, I assume it's naked like us for cost? but also the Earth/Ground is normally of a smaller size/diameter than the Live and Neutral.

But I would be interested in there is some other thinking behind the ground being bare. I mean I have known people in the UK say it's for safety incase a nail is driven into the cable.
 
Thanks for the info.

Thanks, I assume it's naked like us for cost? but also the Earth/Ground is normally of a smaller size/diameter than the Live and Neutral.

But I would be interested in there is some other thinking behind the ground being bare. I mean I have known people in the UK say it's for safety incase a nail is driven into the cable.
The ground is the same size as the conductors because you can’t derate the ground until you reach 40 amps or more.
 
Thanks, I assume it's naked like us for cost? but also the Earth/Ground is normally of a smaller size/diameter than the Live and Neutral.
The ground size depends on the adiabatic limit and for that the USA has had less demanding specs than the UK for some time, so as @Megawatt says reduced CPC size is only for quite big cables. Similar to the EU in that respect.

The UK has long favoured fuses as OCPD and they are very good at limiting the I2t let-through, also our design requierments on Zs to guarantee the disconnection time also is a factor in keeping I2t down due to the short 't' value and they are rather more onerous than EU/USA.
But I would be interested in there is some other thinking behind the ground being bare. I mean I have known people in the UK say it's for safety incase a nail is driven into the cable.
I think it is partly cost (not just the PVC needed, but the resulting size and weight for shipping), and partly to make the cable smaller so easier to work with.

If you nail a cable it is pot-luck as to what you hit anyway. I think the bigger safety aspect is the E/CPC between the live conductors so less likely to get L-N fault and so more chance of RCD picking up damage due to rodent chewing, etc. But that is more speculation.
 
In Ireland the CPC is now insulated and the same size - I believe.
And in Australia and New Zealand they have Twin and Earth with a fully insulated earth / cpc / ground

What is interesting in America / Canada they leave the copper ground wire bare , where as we over sleeve it
 
I mean it is kind of worksite speculation but there is a little bit of truth that it adds safety. If the Live or Neutral insulation are damaged they automatically come into contact with the bare CPC. Metal enclosures are kind of automatically earthed.

But I agree and have always been taught it's because of cost.
 
I mean it is kind of worksite speculation but there is a little bit of truth that it adds safety. If the Live or Neutral insulation are damaged they automatically come into contact with the bare CPC. Metal enclosures are kind of automatically earthed.

But I agree and have always been taught it's because of cost.
This kind of speculation has led some people to believe that it's a requirement for all cables to contain a CPC. (Even on this forum!)
As you say, the only real design advantage is the reduced cost.
 
Amongst the countries that use a flat cable:

USA: Bare earth, same CSA as line conductor
AUS/NZ/IE/RU: Insulated earth, same CSA as line conductor
UK: Bare earth, reduced CSA
JP: Insulated earth, reduced CSA

Japan is about the only example I can find with a smaller, insulated earth. Granted, they don't often use it and it's strange in other ways (the green CPC is bonded down the outside of the other two so it can be zipped off at the terminations). But it sort-of completes the square of permutations.

Obviously there are countries / systems that normally use round cables, such as NYM-J in Europe, where the earth is usually insulated and same size.
 
Amongst the countries that use a flat cable:

USA: Bare earth, same CSA as line conductor
AUS/NZ/IE/RU: Insulated earth, same CSA as line conductor
UK: Bare earth, reduced CSA
JP: Insulated earth, reduced CSA

Japan is about the only example I can find with a smaller, insulated earth. Granted, they don't often use it and it's strange in other ways (the green CPC is bonded down the outside of the other two so it can be zipped off at the terminations). But it sort-of completes the square of permutations.

Obviously there are countries / systems that normally use round cables, such as NYM-J in Europe, where the earth is usually insulated and same size.
Great bit of info 👍
 
The interesting thing with Romex is the outer sheath / jacket is much harder than our PVC , it looks more like LSF cable.
I wonder if it has similar properties to LSF / LS0H cable
 
I've said it before but the old White sheath stuff seems tougher to me.

There was some old White sheath - Black and Red stranded resting on a hot pipe for about 20years and it had hardly done anything to it - would probably be ok for another 20. I suspect the Grey wouldn't have lasted.
 
I've said it before but the old White sheath stuff seems tougher to me.

There was some old White sheath - Black and Red stranded resting on a hot pipe for about 20years and it had hardly done anything to it - would probably be ok for another 20. I suspect the Grey wouldn't have lasted.
Could be LSF cable which is much tougher than Pvc
 
At one time non metallic sheathed cable commonly known by the brand name "Romex®" formerly made by General Cable, now made by Southwire, had a 16 AWG ground wire in 12 and 14 AWG sizes, sometime after the adoption of the 1968 NEC, it was required that the grounding conductor in 10,12,14, AWG sizes that the grounding conductor be the same size as the insulated conductor in those sizes, 6 and 8 AWG NM cable have a 10 AWG grounding conductor, my house which was built in a factory in 1943, was wired with a early NM cable, plated copper conductors, insulated with rubber, covered in cloth, with a spiral paper wrap over each individual conductor, jute string fillers wrapped with a asphalt covered cloth sheathing, the stuff is still in pretty good shape considering how many years since it was manufactured, although it's been of service since around 1980.
 
Pretty much all YOuTube sparks in America and Canada refer to that cable as ROMEX , which I believe is a brand name. It is much harder than pvc twin and earth , it is much more like our LSF cable. Yes the NM stands for Non Metalic.
It comes in a wide variety of gauges much like our twin and earth does where the line and neutral come sheathed and with a bare copper earth / cpc / ground wire.
Yes it is always flat with The main difference being they have a White for Neutral and Black/Very dark grey for Live.
Also from what I can tell you are not allowed to wire Romex surface mounted , it must either be in the fabric of the building Or run in a conduit.
This guy waffles a fair bit and even muddles up his colours but he explains the different sizes , and colours of Romex common in his area

As an American electrician since 1986, I've never actually encountered the brand name "Romex" although that is what everyone calls it. Just like cotton swabs are called Q-tips and adhesive bandages are called Kleenex Our code calls it NM for non-metallic sheathed cable. Prior to the 90's the outer sheath was any color, I've seen white, black, and power blue and tan, but most of it was all just white, come manufacturers would use black for their larger gauges.
American / Canadian terminology for everything is so bizarre, not to mention they can mix lighting and receptacles ( sockets ) on the same circuit and can have receptacles ( sockets ) in bathrooms

also the fact the the bigger the gauge on the wire the smaller it actually is , this had be stumped for ages when watching American YouTube stuff.

In the US and Canada we use radial circuits only, no ring mains. And we don't have fuses in our plugs, save for some holiday decorations which typically use such small gauge wire they must fuse is lower than our receptacles 15 or 20 amp circuits.
Thanks for the info.

Thanks, I assume it's naked like us for cost? but also the Earth/Ground is normally of a smaller size/diameter than the Live and Neutral.

But I would be interested in there is some other thinking behind the ground being bare. I mean I have known people in the UK say it's for safety incase a nail is driven into the cable.

Cost is likely a factor but I've never seen an NM cable with an insulated ground wire. I have seen MC cable, which is a steel or aluminum clad cable which does insulate the ground with green, but that cable was first introduced to cater to the hospitals which by code requires insulation on the ground.
yes There used to be some god awful pvc in the big DIY sheds that was white and near impossible to strip. it was the worst cable every produced
We do have a PVC based NM cable called "UF" which stands for underground feeder, allowed for direct burial which is a bear to strip. NM cable is quite easy to strip (or un-sheath) but UF is more like the PVC was poured around the insulated conductors and ground, whereas NM cable's sheath is more like a hollow flexible tube.
 

Reply to Twin and Earth American style in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
18 months ago I bought American style fridge freezer (this model). I have a two year warranty. I have already had two call outs to replace a...
Replies
15
Views
549
Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
865
Hi, I am involved in a local charity which is fundraising to restore a local pub into a community hub (and also a pub). The pub which is The Hop...
Replies
0
Views
398
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock