Discuss Type S RCD Polarity Clarification in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Given the RCD pictured below


1710411421136.png


With the manufacturers instructions here:
1710411525099.png


Am i right in interpreting that as well as being able to bring the incoming feeds into the bottom, i can also switch the LIVE and Neutral sides over, so that this arrangement would be possible? Forigve the crudity of the drawing

1710411637038.png


The thing that gives me some doubts is the manufactures stamp on the RCD on the top left.

1710411715697.png
 
Yes, it seems the RCD is symmetric in both ways so it could be used like you show.

However, would it not be better to take the supply from the busbar via your 50A MCB and then you can wire the delay RCD up the normal L/N way?

Top/bottom feed is immaterial here as the MI says, however, keeping L wire to the L-marked terminal is in keeping with the "principle of least astonishment".
 
Yeah, you make a good point, i'm so used to switches/protection/surge on the right and overcurrent to their left it didnt even enter my brain until you said it lol.

Saves scraping of the L and using a sharpie on the other side..
 
Yeah, you make a good point, i'm so used to switches/protection/surge on the right and overcurrent to their left it didnt even enter my brain until you said it lol.

Saves scraping of the L and using a sharpie on the other side..
Just out of curiosity has that tnc-s earthing
 
Your drawing suggests that you might be modifying the DB beyond the manufacturer's design specification. If so, this could see you in breach of 536.4.203 so that you effectively become the manufacturer of the complete assembly with its attendant liabilities.
 

Reply to Type S RCD Polarity Clarification in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
676
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
985
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi First post and I'm a DIY-er so apologies if this is the wrong forum to start with. I have a project at the moment that involves replacing a...
Replies
50
Views
7K
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top