Currently reading:
When electrics go wrong!!!

Discuss When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

Darkwood

Staff member
Mod
Esteemed
Arms
Supporter
Reaction score
10,220
Just setting up a new sticky thread that unlike the dodgy trade pics thread is focused on showing the result of failures in electrical installations IE - damage caused which may be due to various reasons. Please do not post pics of poor workmanship if there is nothing else to show like the consequences, use the dodgy pics thread for that.

I will start off below with an example. I am hoping the fresh faced members and inexperienced can get a visual incite of what to expect when you come across such things and how to understand what has occured.
 
Got a call out yesterday afternoon. Told electrics had tripped, turned back on and keeps tripping every few minutes so could I come and check as had no power to sockets, kitchen and half the house.

Arrived to find the following:

95F591D5-0ADF-44D3-9260-4482BB9580F2.jpeg
1E579835-39E6-4EA0-8905-E83F0A81DC28.jpeg
6EE183AD-F973-4447-AEC8-6A8E29CF3D32.jpeg


Basically the far right breaker was a 50A supply to a second DB for one half of the house (big old farmhouse) which includes a 10.5kw shower, sockets, immersion and lights. Also 2 x 32a socket circuits (one of which was the kitchen) a 20a socket circuit and 16a second immersion.

All hanging off a 63a RCD and the board had never been checked in the 18yrs since it was installed.

So I managed to give them some power back. But told them they need a new board now asap and a full EICR doing, as I wouldn’t change a board without doing it anyway (especially not on house where I’ve been called to a melted board) and investigation was needed to check why that 50A breaker had obviously also overheating given the melted plastic around the busbar connection.
 
Received from customer:

View attachment 94306

Going to see it later today, apparently the fitting says "Made in West Germany" on it, so first question is how many others they have.
Second question is what that taped up wire is doing.
Taped wire will be the permanent live for if this was to be an emergency light. Currently (hopefully!) choc-blocked and then taped.
 
The Berlin Wall fell in ‘89 I think… all thanks to knight Rider himself, David Hasselhoff.
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.
 
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.

You'd need to go for a week just to listen to one Pink Floyd song though!!
 
Shop in Dublin had refurb carried out end of last summer. New 35mm tails connected into old panel. Clearly someone didn't check their final connections. The same idiot also managed to break nearly every single cover on the terminals across every panel.
 

Attachments

  • 20210705_082550.jpg
    369.2 KB · Views: 151
  • 20210705_082421.jpg
    341 KB · Views: 186
Call out to loss of power on house ring main, further conversation with owner , they had various sockets lowered from switch height to low level downstairs only a month back by a electrician, said electrician as been back to find the cause but had to leave without solving issue. Although he did disconnect the live and neutrals from fuse board so he got some power back on . That was 3 weeks ago. Said Rfc controls the combi so no heating/hot water and extension leads to various rooms to keep going.
After few tests got open circuit on neutrals and neutral live earth faults. After a bit of bashing nice new painted and fresh plastered walls where the old sockets used to be .Found 4 joints in wall in wagos taped up behind channel. One burnt out giving me the short and another poor joint giving me the open circuit. Ko boxes fitted and blank plates over top new joints.
 

Attachments

  • IMG_0281.JPG
    429.5 KB · Views: 133
  • IMG_0282.JPG
    422.9 KB · Views: 119
  • IMG_0283.JPG
    370.6 KB · Views: 128
Could be worse, could be all metal conduit, threaded into the fittings, and needing half a mile* of other stuff removing before you get back to that one. Of course, I'm guessing they've used male adapters rather than female adapters with bushes.

* Exaggerated for effect.
In this case it's male adaptors with lock rings both sides and there's another 5 of these fittings 2m apart probably all connected the same way, with singles for another lighting circuit running uninterrupted through all of it....
But yes, at least it isn't galv....!
 
In this case it's male adaptors with lock rings both sides and there's another 5 of these fittings 2m apart probably all connected the same way, with singles for another lighting circuit running uninterrupted through all of it....
But yes, at least it isn't galv....!

Male pvc adapters are terrible. Badly designed with terrible lock rings and, for the most part, much less practical than their female counterparts. I dislike them intensely.
 
Male pvc adapters are terrible. Badly designed with terrible lock rings and, for the most part, much less practical than their female counterparts. I dislike them intensely.
I have a similar pair of strippers.
I think you two better meet up......for a chat, of course...
 

Reply to When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top