Search for tools and product advice,

Discuss Whole Kitchen wiring diagram advice (excluding lights) in the DIY Electrical Advice area at ElectriciansForums.net

benhurr

DIY
Reaction score
10
Hi everyone,
please advice and comment on the attached wiring diagram for a kitchen.
There are mixed opinions on the need for FSU-s and number of circuits required.
Distance to cu – 8m running under timber floor. kitchen size – 3.5M X 2.5M
 

Attachments

  • kitchen_wiring2.png
    37.8 KB · Views: 43
Last edited:
You have a lot of fairly high power appliances on one ring there. I would definitely makes some changes to that arrangement.
 
You have a lot of fairly high power appliances on one ring there. I would definitely makes some changes to that arrangement.
I did some amendments: split in 2 rings (top sockets and appliances separately from bottom ones) and split hob and cooker
 

Attachments

  • kiwa4.png
    38.6 KB · Views: 25
Out of interest are you designing, installing and certifying this work yourself or will someone else be involved?
 
Out of interest are you designing, installing and certifying this work yourself or will someone else be involved?
Someone else, but he already disagrees with you regarding the splitting of the ring c.
So
"Out of interest"
3rd opinion is always welcome. (4th as well))
 
sockets were upside down, otherwise any other worries?
 

Attachments

  • kiwa5.png
    84.8 KB · Views: 22
sockets were upside down, otherwise any other worries?

Not sure your sparky is going to be too keen on you changing his design?
 
Someone else, but he already disagrees with you regarding the splitting of the ring c.
So

3rd opinion is always welcome. (4th as well))
4th opinion from Screwfix forum: 2 rings not necessary, only recommended separate circuit for hot tap. He also thinks hob and oven can be together. Basically he is partially agrees with my local el-cian ( agrees on 1rc , but disagrees on oven/hob separation).
3 elcians – 3 different opinions
 
Last edited:
4th opinion from Screwfix forum: 2 rings not necessary, only recommended separate circuit for hot tap. He also thinks hob and oven can be together. Basically he is partially agrees with my local el-cian ( agrees on 1rc , but disagrees on oven/hob separation)

Personally I'd get another electrician to give you a quote and see what their opinion is.
 
are you going to change your mind if he will disagree with you?)) unlikely

Personally no, I wouldn't change my mind. But I'm only one person.

Hopefully some other members will give their opinion on your original arrangement.
 
Hi everyone,
please advice and comment on the attached wiring diagram for a kitchen.
There are mixed opinions on the need for FSU-s and number of circuits required.
Distance to cu – 8m running under timber floor. kitchen size – 3.5M X 2.5M
To be honest, that's a very poorly designed system both practically and technically.
 
Personally no, I wouldn't change my mind. But I'm only one person.

Hopefully some other members will give their opinion on your original arrangement.
so the ring is being split in 2 and your still find it original? I can see, some suggest putting boiler on separate C, and frfreezer on separate C. This way I will run out of space in CU pretty soon.
 
so the ring is being split in 2 and your still find it original? I can see, some suggest putting boiler on separate C, and frfreezer on separate C. This way I will run out of space in CU pretty soon.

You were still saying people were disagreeing with my opinion though.

You really need a proper sparky to design this rather than tinkering with stuff yourself. There's no shame in knowing your limitations.
 
there are 2 things playing on my mind here.

1. as a contractor, I am happy when i have a clear design brief.
this should include the rating of any fixed appliance's and in the case of a kitchen, any other high power device's that are likely to have a permanent home. (microwave, kettle, toaster, washing machine, dishwasher etc.)

I would generally not expect a customer to be particularly interested in the precise layout of the circuits, however i would lay it out on the quote, how many circuits and there rating and use.
i.e.
1 Induction Hob supply 32A
2 cooker and microwave supply 32A
3 general sockets ring 32A
4 waste disposal and boiling water tap 20A

if the customer decided they wanted 2 rings of sockets or the microwave and cooker on different supplies, then i would re quote.
if they want every socket on its own 20A radial then its fine by me but the price is steadily climbing.

2.
if you are arguing about what is the right way to wire your kitchen with the electrician at the quotation stage, the customer/contractor relationship is already broken.

as a contractor we should be providing what the customer wants
however sometimes the customer wants something that is either not possible or cost effective and this needs to be pointed out early on.
i.e. yes of course i can put everything on a separate circuit but it will be £800 more, why not do it this way instead?

sometimes customers have too much time on there hands to read things on the internet about electrical installation that sounds great but is at best misinformed and at worst downright dangerous.

sometimes contractors are simply bad at there job and sometimes the good (technically) ones have a chip on their shoulder and cant deal with a customer wanting it done their way because that's not how they wanted to do it.

a realy good contractor should be able to deal with both the technicality's of providing a safe and good quality installation whilst also having the ability to deal with customers, even the difficult ones, in a professional way.

p.s. some customers can make the last comment impossible but i am not suggesting that you are one of them.
 
You were still saying people were disagreeing with my opinion though.

You really need a proper sparky to design this rather than tinkering with stuff yourself. There's no shame in knowing your limitations.
yet you are not admitting you own:))), first you should obey your own logic then you can preach
 
so the ring is being split in 2 and your still find it original? I can see, some suggest putting boiler on separate C, and frfreezer on separate C. This way I will run out of space in CU pretty soon.
As a rule we're pretty relaxed on here about DIY'ers because generally speaking they tend to be genuinely asking for advice, however all you seem to be wanting to do is find validation for your own [very limited and ill-advised] viewpoint??

I'm also very much inclined to think that you're about to do this work yourself and CLEARLY do not possess the understanding to do so safely. Had you have started this conversation by saying something like "I'm not sure my electrician is very experienced because they're suggesting....." then we could be better able to help you. However attempting to pit a set of armchair Screwfix opinions against a forum of extremely skilled and experienced electricians and electrical engineers isn't really going to get you very far.
 
yet you are not admitting you own:))), first you should obey your own logic then you can preach

I don't understand what you mean, sorry.

Anyway, I've given my opinion. Hopefully you can move on with a suitable sparky who will design, install and test a suitable solution.
 
there are 2 things playing on my mind here.

1. as a contractor, I am happy when i have a clear design brief.
this should include the rating of any fixed appliance's and in the case of a kitchen, any other high power device's that are likely to have a permanent home. (microwave, kettle, toaster, washing machine, dishwasher etc.)

I would generally not expect a customer to be particularly interested in the precise layout of the circuits, however i would lay it out on the quote, how many circuits and there rating and use.
i.e.
1 Induction Hob supply 32A
2 cooker and microwave supply 32A
3 general sockets ring 32A
4 waste disposal and boiling water tap 20A

if the customer decided they wanted 2 rings of sockets or the microwave and cooker on different supplies, then i would re quote.
if they want every socket on its own 20A radial then its fine by me but the price is steadily climbing.

2.
if you are arguing about what is the right way to wire your kitchen with the electrician at the quotation stage, the customer/contractor relationship is already broken.

as a contractor we should be providing what the customer wants
however sometimes the customer wants something that is either not possible or cost effective and this needs to be pointed out early on.
i.e. yes of course i can put everything on a separate circuit but it will be £800 more, why not do it this way instead?

sometimes customers have too much time on there hands to read things on the internet about electrical installation that sounds great but is at best misinformed and at worst downright dangerous.

sometimes contractors are simply bad at there job and sometimes the good (technically) ones have a chip on their shoulder and cant deal with a customer wanting it done their way because that's not how they wanted to do it.

a realy good contractor should be able to deal with both the technicality's of providing a safe and good quality installation whilst also having the ability to deal with customers, even the difficult ones, in a professional way.

p.s. some customers can make the last comment impossible but i am not suggesting that you are one of them.
Interesting idea regarding the split groups. I can see by the amount of opinions this is more like art than precise science. Thank you for your input. Regarding "2" I just need different opinions from professional as I have being let down by them occasionally
 
I don't understand what you mean, sorry.

Anyway, I've given my opinion. Hopefully you can move on with a suitable sparky who will design, install and test a suitable solution.
Pardon me, This Was regarding your notes about "limit of knowledge", you admitted that you would do not want to change your opinion regardless if there will be conflicting information coming from more qualified electrician, so this mean you where ashamed to admit limit of your own knowledge (potentially) . And yet you are asking others to be shameless in this regard ;)
 
Interesting idea regarding the split groups. I can see by the amount of opinions this is more like art than precise science. Thank you for your input. Regarding "2" I just need different opinions from professional as I have being let down by them occasionally
What I posted was NOT a recommendation as to how I would lay out your circuits, just an example of how I would deal with quoting for a kitchen fit out.

Take no notice of me, I am not even registered to provide part P certification so cant be bright enough to do domestic installations.

however I do know a bit about electrics and the ins and outs of customer/contractor relationships and that was where my post was aimed at.
 
Pardon me, This Was regarding your notes about "limit of knowledge", you admitted that you would do not want to change your opinion regardless if there will be conflicting information coming from more qualified electrician, so this mean you where ashamed to admit limit of your own knowledge (potentially) . And yet you are asking others to be shameless in this regard ;)

Look, your original idea was not good. I advised there were two many high power appliances on the one ring circuit, which I stand by. Others also agreed with this.

It's no good you just tinkering around with things when you aren't aware of the regulations or reasoning behind them.

If someone wants to disagree with me then I'm fine with that. As I said, I only one person.

Up to you. Feel free to 'design by screwfix forum' if you wish.
 
Look, your original idea was not good. I advised there were two many high power appliances on the one ring circuit, which I stand by. Others also agreed with this.

It's no good you just tinkering around with things when you aren't aware of the regulations or reasoning behind them.

If someone wants to disagree with me then I'm fine with that. As I said, I only one person.

Up to you. Feel free to 'design by screwfix forum' if you wish.
it was not just Screwfix but local qualified certified electrician as well, the only change he made is splitting hob and oven. there is an updated version of diagram with 2 c rings and separate hob/oven. Yet you don't want to admit your own limitations. And should I state the obvious that anyone who is asking for advice here in diy section is admitting his limitation by definition. please
 
Last edited:
Hi everyone,
please advice and comment on the attached wiring diagram for a kitchen.
There are mixed opinions on the need for FSU-s and number of circuits required.
Distance to cu – 8m running under timber floor. kitchen size – 3.5M X 2.5M

Is this a !960s house ?

I agree with DPG about the single ring main.



Fridge /freezer
Hot tap
Boiler
Ideally, should be on their own circuits

If you're running out of Cu ways, you could always add a small kitchen Cu and have more radial circuits.
 
it was not just Screwfix but local qualified certified electrician as well, the only change he made is splitting hob and oven. there is an updated version of diagram with 2 c rings and separate hob/oven. Yet you don't want to admit your own limitations. And should I state the obvious that anyone who is asking for advice here in diy section is admitting his limitation by definition. please
Competent or qualified ? As there is a big difference.
 
Is this a !960s house ?

I agree with DPG about the single ring main.



Fridge /freezer
Hot tap
Boiler
Ideally, should be on their own circuits

If you're running out of Cu ways, you could always add a small kitchen Cu and have more radial circuits.
ideally I would live on Tenerife :) what is Within regs is fine by me for now ( the house is 1890s))
 
Is this a !960s house ?

I agree with DPG about the single ring main.



Fridge /freezer
Hot tap
Boiler
Ideally, should be on their own circuits

If you're running out of Cu ways, you could always add a small kitchen Cu and have more radial circuits.
thank you! is this any closer to ideal?:kiwa7.png
 
Ideally, every appliance would be on its own dp rcbo.
Dishwasher/tumble dryer/washing machine etc would have isolator switch feeding single socket, not fcu.
i assume in this case isolator switch only required if the socket is behind the appliance and not easily accessible, otherwise why isolator if there is accessible plug? Or is it for extra safety due to water and steam additional hazard? and there were no fcu's on diagram next to appliances , only on integrated microwave because I assume it will come without plug. so just to recap: If it is not on a single socket on diagram it means the appliance is coming without plug. Not all appliances are purchased yet so this part is variable at the moment. All those switches be inside cabinets (within 2 meters from relevant appliance) kiwa8.png
 
Might as well give my thoughts I guess.
In principle I do agree that more circuits is better, as it gives more selectivity between loads. So if one part of the installation becomes faulty, other parts remain intact and in service.

But I also believe in simplicity where possible.

One thing you need to change is having the fridge freezer on A 6 amp MCB. It may only have a small running current, but when the compressor(s) start there is a significant startup surge which will trip a 6A MCB.

The sort of thing that even a competent DIYer will probably not be aware of.

Installation design, even at a relatively simple level, is in my opinion beyond the scope of DIY, because there are so many factors that need to be coordinated, and a huge book of regulations that are applicable and need to be adhered to.
 
I assume it will come without plug.
The UK Plugs and Sockets Regulations require appliances (rated under 13A) to be fitted with plugs by the manufacturers.
It was prompted by the number of accidents caused by people fitting their own plugs! There are exceptions, but you will find when you buy your appliances pretty well all, other than a high current hob, will be fitted with a moulded on plug. (Which brings another complication - if you cut that plug off, and the appliance is subsequently faulty, you may well get told that the warranty is void because you cut the plug off, which is rubbish, but still seems to be a prevalent thing)

 
The UK Plugs and Sockets Regulations require appliances (rated under 13A) to be fitted with plugs by the manufacturers.
It was prompted by the number of accidents caused by people fitting their own plugs! There are exceptions, but you will find when you buy your appliances pretty well all, other than a high current hob, will be fitted with a moulded on plug.

Yes indeed. I'd forgotten about this. And it would seem so have some manufacturers of appliances. I had a 2.3kW oven to fit the other day that didn't come with a plug. In fact the flex had a label wrapped around it stating "do not fit a plug".
 
Last edited:
The UK Plugs and Sockets Regulations require appliances (rated under 13A) to be fitted with plugs by the manufacturers.
It was prompted by the number of accidents caused by people fitting their own plugs! There are exceptions, but you will find when you buy your appliances pretty well all, other than a high current hob, will be fitted with a moulded on plug. (Which brings another complication - if you cut that plug off, and the appliance is subsequently faulty, you may well get told that the warranty is void because you cut the plug off, which is rubbish, but still seems to be a prevalent thing)

Esther Rantzen's finest work!
 
Yes indeed. I'd forgotten about this. And it would seem so have some manufacturers of appliances. I had a 2.3kW oven to fit the other day that didn't come with a plug. In fact the flex had a label wrapped around it starting "do not fit a plug".

I've a feeling it excludes items which are intended for installation by an electrician. But any appliance which is for immediate use by the general public must be fitted with a plug*. Not 100% on this though so happy to be proved wrong.

*plugtop, but don't say it 3 times!
 
I've a feeling it excludes items which are intended for installation by an electrician. But any appliance which is for immediate use by the general public must be fitted with a plug*. Not 100% on this though so happy to be proved wrong.

*plugtop, but don't say it 3 times!
The regulations seem, to my non-legal eye, to apply to any appliance for domestic use that is fitted with a Flex!
But then as you say there is a list of exclusions at the end, and I think number 7 tallies with your feeling.
IMG_0388.jpeg
 
The regulations seem, to my non-legal eye, to apply to any appliance for domestic use that is fitted with a Flex!
But then as you say there is a list of exclusions at the end, and I think number 7 tallies with your feeling.
View attachment 111844

Many thanks - that's what I had in mind. Makes sense that there had to be an exclusion to cover things like this.
 
Might as well give my thoughts I guess.
In principle I do agree that more circuits is better, as it gives more selectivity between loads. So if one part of the installation becomes faulty, other parts remain intact and in service.

But I also believe in simplicity where possible.

One thing you need to change is having the fridge freezer on A 6 amp MCB. It may only have a small running current, but when the compressor(s) start there is a significant startup surge which will trip a 6A MCB.

The sort of thing that even a competent DIYer will probably not be aware of.

Installation design, even at a relatively simple level, is in my opinion beyond the scope of DIY, because there are so many factors that need to be coordinated, and a huge book of regulations that are applicable and need to be adhered to.

Might as well give my thoughts I guess.
In principle I do agree that more circuits is better, as it gives more selectivity between loads. So if one part of the installation becomes faulty, other parts remain intact and in service.

But I also believe in simplicity where possible.

One thing you need to change is having the fridge freezer on A 6 amp MCB. It may only have a small running current, but when the compressor(s) start there is a significant startup surge which will trip a 6A MCB.

The sort of thing that even a competent DIYer will probably not be aware of.

Installation design, even at a relatively simple level, is in my opinion beyond the scope of DIY, because there are so many factors that need to be coordinated, and a huge book of regulations that are applicable and need to be adhered to.
this is easy fix, I couldn't find specs for my fridge, and too lazy to pull it as all info at the back regarding load. Let's have 13A mcb then for a fridge circuit in a perfect scenario. I still inclined to put all exept hob/oven/ hot tap on 1 ring c. But still wondering what is the perfect wiring, how far will you go, guys
 
this is easy fix, I couldn't find specs for my fridge, and too lazy to pull it as all info at the back regarding load. Let's have 13A mcb then for a fridge circuit in a perfect scenario. I still inclined to put all exept hob/oven/ hot tap on 1 ring c. But still wondering what is the perfect wiring, how far will you go, guys

13A MCB? Maybe a 13A fuse in an FCU. Feb by a suitable MCB and cable obviously.

This is still in the 'design by forum' method though. I'm reluctant to give step by step advice as this would be against the forum guidelines.
 
13A MCB? Maybe a 13A fuse in an FCU. Feb by a suitable MCB and cable obviously.

This is still in the 'design by forum' method though. I'm reluctant to give step by step advice as this would be against the forum guidelines.
getting all sоur again, no one sane will build this over-designed circuit, I remind you this is your "dream circuit" now. Fridge plug has 13A fuse. The other electrician up the lines said no need for fcu, just isolator and single plug. All wires apart from the hob are 2.5mm. You can't agree between each other on what is right and you are still discovering regulations while we speak. So no point to be snobbish here
 
getting all sоur again, no one sane will build this over-designed circuit, I remind you this is your "dream circuit" now. Fridge plug has 13A fuse. The other electrician up the lines said no need for fcu, just isolator and single plug. All wires apart from the hob are 2.5mm. You can't agree between each other on what is right and you are still discovering regulations while we speak. So no point to be snobbish hear

I was questioning your idea of a 13A MCB. And I suggested an alternative, ie. a 13A fuse, whether that is in a plug or an FCU. But if you want to get hold of a 13A MCB then fair enough.

To be honest I think you're taking the mick a bit by expecting people to design your system for you and then being rude when they disagree with either you or your 'first electrician'.

And for that reason....... I'm out.
 
Last edited by a moderator:
I was questioning your idea of a 13A MCB. And I suggested an alternative, ie. a 13A fuse, whether that is in a plug or an FCU. But if you want to get hold of a 13A MCB then fair enough.

To be honest I think you're taking the p*** a bit by expecting people to design your system for you and then being rude when they disagree with either you or your 'first electrician'.

And for that reason....... I'm out.
thank you for you generous input, indeed 13A mcb are not common, that was a typo on a diagram. Also I just checked the similar fridge is 2.7kw so 16a mcb is good. As for isolator (fused or not) it is only needed if plug is not accessible (behind appliance, the fridge cable is long enough to put socket in near cabinet) or not? I've got it, those plugs are mostly down to personal preferences and additional safety and convenience for servicing. Otherwise those are not necessary (if socket is accessible)
IET - BS 7671 On-site Guide (2018): "Appliances built into kitchen furniture (integrated appliances) should be connected to a socket-outlet or switch fused connection unit that is accessible when the appliance is in place and in normal use. Alternatively, where an appliance is supplied from a socket-outlet or a connection unit, these should be controlled by an accessible double pole switch or switched fused connection unit."
 
Last edited:
what if we keep part of main (whole house) ring circuit which is currently passing through the room for everything above worktops: like microwave, hood, boiler, and 2/3 double sockets. this way the worse case scenario total load for dedicated kitchen ring circuit will be under 32A . If we consider 1,76kw multicooker (used often), 1.2kw blender and 1.1kw mixer (occasionally) on above worktop sockets this could help to balance the load but might be more confusing for testing and CU labelling or is it very bad practice in your opinion?kiwa91.jpg
 
what if we keep part of main (whole house) ring circuit which is currently passing through the room for everything above worktops: like microwave, hood, boiler, and 2/3 double sockets. this way the worse case scenario total load for dedicated kitchen ring circuit will be under 32A . If we consider 1,76kw multicooker (used often), 1.2kw blender and 1.1kw mixer (occasionally) on above worktop sockets this could help to balance the load but might be more confusing for testing and CU labelling or is it very bad practice in your opinion?View attachment 111862
I think most people on here will know about diversity, division of circuits etc.
The way forward for you is to discuss this with your electrician.
 

Reply to Whole Kitchen wiring diagram advice (excluding lights) in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good Morning need some advice please. Yesterday went to change a light fitting in hallway. There are two ceiling lights in the hall controlled by...
Replies
6
Views
270
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
608
Hello. I am new to wiring and could use some help getting this circuit wired in the kitchen . I am trying to get the source power to the GFCI and...
Replies
1
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock