Discuss 3 phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi everyone,

I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection.

The client has specifically asked for them to be plug and play and rcd protected, which is fine as they are under 32amps.

I will be running in 5 core swa's for future proofing, but in regards to RCD protection, has anyone fitted the 3Phase RCCB from Doepke which dosnt require a neutral?




I have been asked to pull in some new supplies for some 3 phase
 
I suppose the three phase voltages will have a sum of zero.
<= This

The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a sensing point of view if it is fitted or not. But sometimes the test button might need N, though many 4P RCD go L-L to avoid that situation.

However, fitting 3P+N+E is just far more future-proof !
 

Reply to 3 phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
277
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
863
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
10
Views
776
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
388

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock