Currently reading:
UK 3 phase rcd protection

Discuss 3 phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi everyone,

I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection.

The client has specifically asked for them to be plug and play and rcd protected, which is fine as they are under 32amps.

I will be running in 5 core swa's for future proofing, but in regards to RCD protection, has anyone fitted the 3Phase RCCB from Doepke which dosnt require a neutral?




I have been asked to pull in some new supplies for some 3 phase
 
I suppose the three phase voltages will have a sum of zero.
<= This

The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a sensing point of view if it is fitted or not. But sometimes the test button might need N, though many 4P RCD go L-L to avoid that situation.

However, fitting 3P+N+E is just far more future-proof !
 

Reply to 3 phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock