A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible?

Discuss A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible? in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
0
I have by mistake used 6amps C grad MCB on a 2000-watt dishwasher. though I was asked to put 10 amps. but it is running properly.
how it is possible and is it safe?

thanking you.
 
Last edited:
If the 2000 watt rating is what it says on the info sticker on the back of the dishwasher then it's the absolute maximum power the machine will ever run at and most of the time the actuial power consumption will be considerably less. Also a 6 A MCB will happily allow 7 or 8 Amps through it without tripping for a good period of time.

All that aside, the MCB is sized to protect the circuit wiring, not the appliance itself. Whether it's safe or not is down to the current rating of the MCB being appropriate for size of the wiring going to the socket outlets.
 

Reply to A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible? in the Electrical Appliances Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top